It would seem that the AHJ has become confused by the verbiage of NFPA 13, 24.1.2.3 (2010 ED) not requiring Hydrostatic testing for modifications to fewer than 20 sprinklers. Call me simple, but the scope of NFPA 25 as outlined in 1.1 (2008 ED) seems pretty transparent as to WHAT must be inspected.
-----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of [email protected] Sent: Thursday, August 21, 2014 9:43 AM To: [email protected] Subject: Re: NFPA 25 2011 System Size REPLY Good morning Ladies/Gentlemen: I do not know where < 20 sprinklers might be found in 25 (or any other standard) and/or why there would be such a stipulation in the first place...That said: IF an overwhelming number of failures attributed to sprinkler systems (all sizes) are due to closed valves and/or inadequate water supplies, it seems 'logical' that, if a sprinkler system has a water supply and/or control valve, those devices would need to be check/tested/inspected, regardless of the number of sprinklers in the system?? The number '20' has been bandied around for years as to adding that number of heads to an existing system, plans submittals, whether a hydro was required, FDC requirement, etc. In my professional (albeit humble) opinion, ALL fire sprinkler systems need to be inspected/tested per NFPA-25 guidelines. I rather suspect our friends in the insurance industry would concur. In New Mexico, it is quarterly - it is statewide (commercial systems). Best to All- Jerry [email protected]_ (mailto:[email protected]) Jerry D. Watts, SFPE President & Co-Founder ACCENT FIRE ENGINEERING INT'L. Ltd.* Santa Fe, New Mexico (a U.S. State) (800) 503.1961 nationwide *Founded 1991 In a message dated 8/21/2014 9:29:26 A.M. Mountain Daylight Time, [email protected] writes: In Seattle the rule was, and may still be but I haven't worked in industry for some time, that a six head or less T.I. didn't require an inspection, but that was local to Seattle. On Thu, Aug 21, 2014 at 5:11 AM, Greg McGahan <[email protected]> wrote: > * NFPA #25.2.1.4* says that modifications affecting less than 20 sprinklers > does not require hydrostatic testing...we regularly have inspections > for 1 > and 2 head mods... > > > Greg McGahan > Living Water Fire Protection, LLC <http://www.livingwaterfp.com> > 1160 McKenzie Road > Cantonment, FL 32533 > 850-937-1850 > fax 850-937-1852 > > > On Wed, Aug 20, 2014 at 2:10 PM, Charles Thurston > <[email protected]> > wrote: > > > Hello Sprinklerforum, > > > > I have been told verbally by an AHJ in the area that systems > > under 20 heads do not have to be inspected. He said it was in the > > code, But has > not > > been able to pinpoint where. I am unable to find that code > reference, > > Anybody know where it would be? > > > > -- > > Best regards, > > Charles mailto:[email protected] > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) A problem well stated is a problem half solved. -Charles F. Kettering, inventor and engineer (1876-1958) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org --- This email is free from viruses and malware because avast! Antivirus protection is active. http://www.avast.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org