It would seem that the AHJ has become confused by the verbiage of NFPA 13,
24.1.2.3 (2010 ED) not requiring Hydrostatic testing for modifications to
fewer than 20 sprinklers.  Call me simple, but the scope of NFPA 25 as
outlined in 1.1 (2008 ED) seems pretty transparent as to WHAT must be
inspected.



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
Sent: Thursday, August 21, 2014 9:43 AM
To: [email protected]
Subject: Re: NFPA 25 2011 System Size REPLY

Good morning Ladies/Gentlemen:
 
I do not know where < 20 sprinklers might be found in 25  (or any other
standard) and/or why there would be such a stipulation in the  first
place...That said: IF an overwhelming number of  failures attributed to
sprinkler systems (all sizes) are due  to closed valves and/or inadequate
water supplies, it seems 'logical' that, if a  sprinkler system has a water
supply and/or control valve, those devices would  need to be
check/tested/inspected, regardless of the number of sprinklers in the
system?? The number '20' has been bandied around for years as to adding that
number of heads to an existing system, plans submittals, whether a hydro was
required, FDC requirement, etc.
 
In my professional (albeit humble) opinion, ALL fire sprinkler  systems need
to be inspected/tested per NFPA-25 guidelines. I rather suspect our friends
in the insurance industry would concur. In New Mexico, it is quarterly - it
is statewide (commercial systems).
 
Best to All-
 
Jerry
[email protected]_ (mailto:[email protected]) 
 
Jerry D. Watts, SFPE
President & Co-Founder
ACCENT FIRE ENGINEERING INT'L. Ltd.*
Santa Fe, New Mexico (a U.S. State)
(800) 503.1961 nationwide
 
*Founded 1991
 
 
 
In a message dated 8/21/2014 9:29:26 A.M. Mountain Daylight Time,
[email protected] writes:

In  Seattle the rule was, and may still be but I haven't worked in industry
for  some time, that a six head or less T.I. didn't require an inspection,
but  that was local to Seattle.


On Thu, Aug 21, 2014 at 5:11 AM, Greg  McGahan <[email protected]>
wrote:

> * NFPA #25.2.1.4*  says that modifications affecting less than 20
sprinklers
> does not  require hydrostatic testing...we regularly have inspections 
> for
1
> and  2 head mods...
>
>
> Greg McGahan
> Living Water Fire  Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie  Road
> Cantonment, FL 32533
> 850-937-1850
> fax  850-937-1852
>
>
> On Wed, Aug 20, 2014 at 2:10 PM, Charles  Thurston 
> <[email protected]>
> wrote:
>
> > Hello  Sprinklerforum,
> >
> >   I have been told  verbally by an AHJ in the area that systems 
> > under 20 heads do not  have to be inspected. He said it was in the 
> > code, But has
> not
>  > been able to pinpoint where.  I am unable to find that code  
> reference,
> > Anybody know where it would be?
> >
>  > --
> > Best regards,
> >  Charles      mailto:[email protected]
> >
> >  _______________________________________________
> > Sprinklerforum  mailing list
> > [email protected]
>  >
> >
>  
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>  >
> _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>
>  
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering  Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA  98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700  (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS,  WSAFM, WFC, WFSC

They are happy men whose natures sort with their  vocations. -Francis Bacon,
essayist, philosopher, and statesman  (1561-1626)

A problem well stated is a problem half solved. -Charles F.  Kettering,
inventor and engineer  (1876-1958)
_______________________________________________
Sprinklerforum  mailing  list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


---
This email is free from viruses and malware because avast! Antivirus protection 
is active.
http://www.avast.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to