Yep, I did go there and that's why I asked because they say "If an ancillary 
product is to come into direct contact with a FlowGuard pipe & fittings system, 
BlazeMaster fire Sprinkler system and/or Corzan industrial system and is not 
included in the FBCT System Compatible Program, Lubrizol recommends that 
chemical compatibility be confirmed with that product's manufacturer prior to 
use." Direct contact being the key I think. 

There doesn't appear to be incompatible cutting oils. Several tested ok.  FM 
approval for pipe internally coated pipes so that seems like less of a problem. 
 There are several sealants not compatible and a few that are compatible.  All 
that is well a good except I can't see anything about indirect contamination.  
So if the existing system has known incompatibles or unknowns is that direct 
contact?   If I drill on a saddle probably don't use any cutting oil. If I use 
the right thread sealant on the new work no problem.  What if any oil is left 
from the original installation, probably not much if any.  Is the thread 
sealant, assuming incompatible or unknown, on the original heads, but not in 
contact with CPVC directly, ok?   

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns & McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of rongreenman .
Sent: Thursday, August 21, 2014 11:23 AM
To: [email protected]
Subject: Re: Mixed Steel and CPVC

Go to Lubrizol and you can find info on this. Simple answer is yea, problem. 
Mitigation,???????



On Thu, Aug 21, 2014 at 9:12 AM, Cahill, Christopher <[email protected]>
wrote:

> I've been out of the CPVC world for many years now.  I noticed a 
> system the other day with what I guess is original steel and 
> remodeling with CPVC.  I was wondering if there are any reasons that is a bad 
> idea?
> Contamination of the CPVC with cutting oil, thread sealant, etc. line 
> of thinking.
>
> Chris Cahill, PE*
> Associate Fire Protection Engineer
> Burns & McDonnell
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]<mailto:[email protected]>
> www.burnsmcd.com<http://www.burnsmcd.com/>
> *Registered in: MN
>
>
> Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work 
> For
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering, inventor 
and engineer (1876-1958) _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to