There WERE such coatings, for sure.  Currently, there are 29 or 30 pipes on the 
market from 5 or 6 mills that are listed by FM and have been rigorously tested 
and affirmed by Lubrizol to be compatible.   The 1st generation anti-microbial 
coatings are problematic, but new piping should be okay.

Steve L.

 




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jim Davidson
Sent: Thursday, August 21, 2014 11:51 AM
To: [email protected]
Subject: RE: Mixed Steel and CPVC

Be very careful if the steel pipe was coated with anti-MIC coatings on the 
internal surface, and determine when the steel pipe was manufactured because 
there are anti-MIC coatings that are not compatibility with CPVC pipe and you 
need to research very carefully since Lubrizol did not fully test all anti-MIC 
coatings.  

The following is from Spears:

SPEARS® MANUFACTURING COMPANY
CORPORATE OFFICE
15853 OLDEN STREET * SYLMAR, CALIFORNIA 91342 MAILING ADDRESS: P.O. BOX 9203 * 
SYLMAR, CALIFORNIA 91392 Telephone (818) 364-1611 * Fax (818) 364-6945  
www.spearsmfg.com

Fire Sprinkler Systems with Anti-MIC Coated Metal Pipe

CPVC piping has been successfully used in combination with copper or steel 
piping for many years when proper attention is given to cutting oils, thread 
sealants and other potentially incompatible materials that can cause 
Environmental Stress Cracking (ESC) in CPVC.
However, certain Anti-Bacterial Corrosion coatings designed to prevent 
Microbiological Influenced Corrosion (MIC) that are applied as a lining to 
metal pipe are at the center of a major ESC problem concerning combination of 
CPVC with Metal fire sprinkler systems. It has been Spears'® experience that 
this issue is primarily concentrated around piping that has been coated with 
ABF® II or certain other aftermarket coatings applied in the field.

Steel pipe manufacturers have indicated that with the changes to one CPVC 
material suppliers "compatibility program", liability has now shifted from the 
CPVC manufacturers to the contractor. In reality, nothing has changed with 
regard to liability. Each party (CPVC and Steel piping manufacturers, 
designers, contractors and owners) must all do their "due diligence", and 
continue to carry the same liability they always have.

While Spears® Manufacturing Company has never provided a CPVC "compatibility 
program", information based on our testing and experience with the 
compatibility of products requested on a case by case basis has been readily 
provided. Based on conclusion of compatibility studies by FM Global in 
conjunction with Spears® ongoing test studies, Spears® accepts the following 
metal pipe products with factory applied MIC prevention coatings for use with 
Spears® FlameGuard® CPVC piping products:
        * Bull Moose Tube Company Eddy Guard II antimicrobial coated sprinkler 
pipe
        * Youngstown Tube Company YTC Guard® antimicrobial coated sprinkler pipe
        * Wheatland Tube Company MIC SHIELD(tm) sprinkler pipe
        * Allied Tube and Conduit metal fire sprinkler pipe coated with "M-Coat"

This acceptance for use is contingent on the proper installation of each 
product with Spears® FlameGuard® CPVC products, in accordance with 
manufacturers' published installation instructions. Testing has shown these 
products to have satisfactory performance in normal installation of CPVC 
products. However, the potential for compatibility problems can be present in 
installations where CPVC materials are highly stressed. Such situations include 
but are not limited to, inadequate compensation for thermal expansion and 
contraction, excessive bending beyond specified limits, improper pipe hanger or 
anchor selection or installation, over tightening of threaded joints, and other 
improper CPVC installation practices yielding high stress loads.

THE FACTS REMAIN: CPVC Nonmetallic Fire Sprinkler Systems offer significant 
advantages:
No Rust, No Microbiologically Influenced Corrosion, Longer Service Life with 
Superior Flow, Ease of Installation and Overall Lower Cost of Ownership when 
compared to the alternative materials available. They are completely acceptable 
and intended for use in hybrid fire sprinkler piping systems when proper 
training, installation, and common sense prevail.
FlameGuard® CPVC Fire Protection products manufactured by Spears® carry our 
standard Limited Lifetime Warranty. AMIC-7-041113

A Spears updaated approved products list is found at this web site: 
http://www.spearsmfg.com/flameguard/FGAPL-7_web.pdf 

This is for Spears products only so you will need to specifically check with 
each pipe manufacturer and be specific about the products you are asking 
questions about including the date of manufacturer.

To add to the confusion this memo was found on the NFSA web site:

Victaulic Memo Adds to CPVC Compatibility Controversy 

A memo circulated by the Victaulic Company on September 12th has added to 
controversy regarding compatibility of CPVC piping with the anti-microbial 
coatings provided for some steel sprinkler piping products. A copy of the 
Victaulic memo can be viewed at (need link here). The memo cites test results 
that contradict those previously reported by the Allied Tube and Lubrizol 
companies. According to Victaulic, an antimicrobial coating mixed with water 
"caused a hydrostatic pressure failure rate four times faster than baselines 
using water alone" in CPVC piping. Based on its testing, Victaulic is 
recommending that steel pipe with antimicrobial coatings not be used in 
combination with CPVC products until such time that an appropriate test 
protocol is developed that would allow issuance of a listing for such 
combination by a product listing laboratory. 

In the August 12, 2008 edition of eTechAlert, NFSA had offered the following 
advice to its contractor members: 

"Given that there is no effort under way to officially list these piping 
products as compatible, NFSA member contractors have asked for guidance as to 
whether they need to be concerned about the use of CPVC downstream of steel 
pipe protected with antimicrobial coatings. Common sense indicates that the 
potential for a problem is greatest when the CPVC is downstream of large 
amounts of coated steel pipe, and when stresses on the CPVC pipe are highest, 
such as in the case of high-rise buildings. As in many other areas of product 
usage, there are shades of gray that will ultimately be sorted out, but 
contractors must use their best judgment until that time." 

NFSA Executive Vice President Russ Fleming notes that if contractors are 
concerned that CPVC could be damaged by upstream steel pipe protected with 
anti-MIC coatings, they can either avoid the use of such piping arrangements or 
at least avoid the possibility that water from the steel piping flows through 
the CPVC piping. This could include the use of alarm test and drain connections 
located at the riser, such that water flowed for testing purposes does not pass 
through downstream CPVC. In such case, however, consideration should also be 
given to the manner in which the CPVC piping is initially filled and 
pressurized. 

As this controversy proceeds, NFSA is addressing it on several fronts. The NFSA 
engineering staff is participating in discussions at the NFPA Committee on 
Sprinkler Installation Criteria, and preliminary efforts in the area of testing 
protocols are being made through the NFSA/UL/FM Standards Review Committee. 

Additional reading go to : http://lubrizol-blazemaster-issues.com/

Have a fire safe day!

Jim


DAVIDSON ASSOCIATES

Fire Protection Engineering     P. O. Box 4010
Code Consultants        Greenville, DE  19807-0010
Medical Gas Systems Engineering (302) 994-9500
        Fax (302) 994-3414

CONFIDENTIALITY
This report and any attachments are confidential and also may be privileged.
If you are not the named recipient, or have otherwise received this report in 
error, please destroy the report, notify the sender immediately, and do not 
disclose its contents to any other person, use them for any purpose, or store 
or copy them in any medium.
Thank you for your cooperation.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Cahill, Christopher
Sent: Thursday, August 21, 2014 1:30 PM
To: [email protected]
Subject: RE: Mixed Steel and CPVC

Yep, I did go there and that's why I asked because they say "If an ancillary 
product is to come into direct contact with a FlowGuard pipe & fittings system, 
BlazeMaster fire Sprinkler system and/or Corzan industrial system and is not 
included in the FBCT System Compatible Program, Lubrizol recommends that 
chemical compatibility be confirmed with that product's manufacturer prior to 
use." Direct contact being the key I think. 

There doesn't appear to be incompatible cutting oils. Several tested ok.  FM 
approval for pipe internally coated pipes so that seems like less of a problem. 
 There are several sealants not compatible and a few that are compatible.  All 
that is well a good except I can't see anything about indirect contamination.  
So if the existing system has known incompatibles or unknowns is that direct 
contact?   If I drill on a saddle probably don't use any cutting oil. If I use 
the right thread sealant on the new work no problem.  What if any oil is left 
from the original installation, probably not much if any.  Is the thread 
sealant, assuming incompatible or unknown, on the original heads, but not in 
contact with CPVC directly, ok?   

Chris Cahill, PE*
Associate Fire Protection Engineer
Burns & McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of rongreenman .
Sent: Thursday, August 21, 2014 11:23 AM
To: [email protected]
Subject: Re: Mixed Steel and CPVC

Go to Lubrizol and you can find info on this. Simple answer is yea, problem. 
Mitigation,???????



On Thu, Aug 21, 2014 at 9:12 AM, Cahill, Christopher <[email protected]>
wrote:

> I've been out of the CPVC world for many years now.  I noticed a 
> system the other day with what I guess is original steel and 
> remodeling with CPVC.  I was wondering if there are any reasons that is a bad 
> idea?
> Contamination of the CPVC with cutting oil, thread sealant, etc. line 
> of thinking.
>
> Chris Cahill, PE*
> Associate Fire Protection Engineer
> Burns & McDonnell
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]<mailto:[email protected]>
> www.burnsmcd.com<http://www.burnsmcd.com/>
> *Registered in: MN
>
>
> Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work 
> For
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering, inventor 
and engineer (1876-1958) _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to