Next time you even start to think of any basis for imposing a velocity of 32 ft/s, take a hammer and smash a finger. Hopefully the pain will divert you from wasting your time especially if you’re assuming you are dealing with facts. I’ve heard numerous conclusion as to why the mystical 32 ft/s existed. Only one has any chance of being valid. Joe Hankins told me long ago that FM initially imposed a velocity restriction after hydraulic calc’s entered the scene and folks started designing gridded storage systems with 1 inch BLs. For ever other basis, I can hear Andy Rooney saying - Have you ever wondered why …...
Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org On Sep 12, 2014, at 5:51 AM, Brad Casterline <[email protected]> wrote: > Damien, will you mail me those snaps too please? I have heard the pipe > schedules were derived by increasing the size when the velocity reached > about 32 ft/sec. Figuring out approximate flow per head and average > densities, etc, will give me something to do as I sit at the kitchen table > and drink beer tonight. Thanks. > > Good luck Jeremy! > > Brad _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org