To answer your original question, I believe it is acceptable. However; I also 
feel this moves you to 13 and needing hydraulics to prove the new valve will 
work since you are not replacing "Like for Like"

R/
Matt

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Monday, November 24, 2014 7:25 PM
To: [email protected]
Subject: Re: Frozen open PIV

Good question. 
Yes we did and we pulled the top off the post as well to verify it was a valve 
issue and not the post. It also was completely covered in ivy leading us to 
believe it had not been exercised for many years despite inspection tags. W

Jeff
JB Fire Protection
Sent from my iPhone

> On Nov 24, 2014, at 18:13, <[email protected]> <[email protected]> 
> wrote:
> 
> Did you check to see if it is a left hand valve? I've run into this in the 
> past. 
> 
> Mark at Aero
> 602 820-7894
> 
> Sent from my iPhone
> 
>> On Nov 24, 2014, at 6:08 PM, "Jeff Bridges" <[email protected]> 
>> wrote:
>> 
>> We have a Post indicator valve that controls a single interior riser.
>> 
>> We discovered during routine testing the PIV is frozen.
>> 
>> The sign indicates it's in the open position and main drain test 
>> shows no abnormalities from previous inspections.
>> 
>> We proposed replacing the PIV and valve- another company proposed 
>> yanking the post, leaving the valve and simply adding a BFV on the riser.
>> 
>> Acceptable alternative?
>> 
>> 
>> 
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> ler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
> 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org