So, it's broke and you/they don't know why?  And you are sure it's going to 
stay broke that way until at least the day after the fire.  Then yep no problem 
abandoning and installing a new valve inside provided the AHJ doesn't require 
PIV's. 

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns & McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For



> 
>> On Nov 24, 2014, at 6:08 PM, "Jeff Bridges" <[email protected]> 
>> wrote:
>> 
>> We have a Post indicator valve that controls a single interior riser.
>> 
>> We discovered during routine testing the PIV is frozen.
>> 
>> The sign indicates it's in the open position and main drain test 
>> shows no abnormalities from previous inspections.
>> 
>> We proposed replacing the PIV and valve- another company proposed 
>> yanking the post, leaving the valve and simply adding a BFV on the riser.
>> 
>> Acceptable alternative?
>> 
>> 
>> 
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> ler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
> 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to