Jerry, I do not believe you need 'ten diameters straight in front of the pump' as long as you use an OSY, pipe and fittings of the diameter required for the rated capacity, and aligned as required to get equal velocity on both sides of the impeller (as you described).
Brad -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Jerry Van Kolken Sent: Monday, January 12, 2015 4:18 PM To: [email protected] Subject: 10 Diameter for Pump supply arrangement I have a project where we are trying to reuse the existing pump pad, but if we do this there will not be a 10 diameters straight in front of the pump. I this an acceptable arrangement for a 12" connection? >From the Pump Flange - Install an elbow facing up, then install roughly a 3'-0" piece of pipe then an another elbow in-line with the pump. Horizontal with a 6'-0" pipe to an elbow facing down. Another pipe vertical to the OS&Y Valve, then the feed from the supply manifold. Jerry Van Kolken Millennium Fire Protection Corp. 101 Copperwood Way, Suite H Oceanside, CA 92058 (760) 722-2722 FX 722-2730 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org