Unless I'm missing something, it doesn't look like to me you are required to
have the 10x pipe diameters.  If your piping is all in-line with the pump
you shouldn't need it.  So when you say front of the pump your talking
suction right?  The only thing that isn't clear, is what the relationship of
the supply manifold to the fire pump.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Jerry Van Kolken
Sent: Monday, January 12, 2015 5:18 PM
To: [email protected]
Subject: 10 Diameter for Pump supply arrangement

I have a project where we are trying to reuse the existing pump pad, but if
we do this there will not be a 10 diameters straight in front of the pump.

 

I this an acceptable arrangement for a 12" connection? 

 

>From the Pump Flange - Install an elbow facing up, then install roughly a
3'-0" piece of pipe then an another elbow in-line with the pump. Horizontal
with a 6'-0" pipe to an elbow facing down. Another  pipe vertical to the
OS&Y Valve, then the feed from the supply manifold.

 

Jerry Van Kolken

Millennium Fire Protection Corp.

101 Copperwood Way, Suite H

Oceanside, CA 92058

(760) 722-2722 FX 722-2730

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to