Correct I meant the suction side of the pump. The supply manifold is running 135 degrees from the pump suction. But we have the 10x Dia in pipe and fittings before the OS&Y which is on the tap off the supply manifold.
Jerry Van Kolken Millennium Fire Protection (760) 722-2722 -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Jeremy Frazier Sent: Tuesday, January 13, 2015 12:30 PM To: [email protected] Subject: RE: 10 Diameter for Pump supply arrangement Unless I'm missing something, it doesn't look like to me you are required to have the 10x pipe diameters. If your piping is all in-line with the pump you shouldn't need it. So when you say front of the pump your talking suction right? The only thing that isn't clear, is what the relationship of the supply manifold to the fire pump. -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Jerry Van Kolken Sent: Monday, January 12, 2015 5:18 PM To: [email protected] Subject: 10 Diameter for Pump supply arrangement I have a project where we are trying to reuse the existing pump pad, but if we do this there will not be a 10 diameters straight in front of the pump. I this an acceptable arrangement for a 12" connection? >From the Pump Flange - Install an elbow facing up, then install roughly a 3'-0" piece of pipe then an another elbow in-line with the pump. Horizontal with a 6'-0" pipe to an elbow facing down. Another pipe vertical to the OS&Y Valve, then the feed from the supply manifold. Jerry Van Kolken Millennium Fire Protection Corp. 101 Copperwood Way, Suite H Oceanside, CA 92058 (760) 722-2722 FX 722-2730 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ______________________________________________________________________ This email has been scanned by the Symantec Email Security.cloud service. For more information please visit http://www.symanteccloud.com ______________________________________________________________________ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org