I have seen this done in the same manner that Mark described, except it was on 
private property. There was a domestic pump that essentially served as a large 
jockey pump. Then the UL listed fire pump would kick in for the larger fire 
sprinkler or fire hydrant demands. 

This particular project was on the east coast about 10-15 years ago. I have not 
seen this done since. The design was conceived by the project engineer. It 
seems to have worked for the situation. 

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Feb 20, 2015, at 7:46 AM, Mark A. Sornsin, P.E. <[email protected]> 
> wrote:
> 
> It sounds like you are in a situation where you need to have a booster pump 
> arrangement for the municipal supply, in this case feeding just this 
> property. I have seen this done in remote areas of usually small towns for 
> this very reason.  In those cases, however, it was a municipally owned pump 
> system. They would have a low-flow pump to supply domestic water at the 
> required pressure; then a high-flow 'fire service' pump that would kick on 
> upon large volume demand. This second pump (or pumps) usually served 
> sprinkler systems and area hydrants.
> 
> I think this can be done but, given that this appears to all be private, I am 
> unclear on the need for listed fire pumps versus standard domestic service 
> pumps. I.e. when is a fire pump a fire pump as opposed to just part of the 
> 'domestic water supply?'
> 
> Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer 
> | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
> http://www.kfiengineers.com
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Todd - Work
> Sent: Friday, February 20, 2015 5:08 AM
> To: [email protected]
> Subject: domestic and fire system.
> 
> I am working on a project where the facility has a private water tank that 
> they want to abandon and connect to the city supply. However, the public 
> supply falls short of the required pressure. The private tank is supplied by 
> connection to the public. The easiest solution would be to build a pump house 
> near where the old tank is and connect to the existing tank feed and yard 
> system (both 8"). However, the system feeds both fire and domestic supplies. 
> Has anybody done one of these successfully? Any thoughts? The location is a 
> hospital and there are 5 fire lead-ins to the building and an unknown number 
> of domestic connections. (Note: the facility isn't that large and the whole 
> thing could have been done with one lead-in and 2 or 3 zones.)
> 
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please visit http://www.symanteccloud.com 
> ______________________________________________________________________
> 
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please visit http://www.symanteccloud.com
> ______________________________________________________________________
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to