Richard,

We go through this all the time in Delaware where the SFMO requires
backflows to be downstream of fire pumps.
There are no backflows listed for pressures higher than 175 PSI that I've
ever seen or heard of.  So a PRV it is.

Your only saving grace might be is if this in Aqua PA territory, they're
going to mandate a PRV anyway.


Benjamin Young

On Tue, Mar 3, 2015 at 6:28 PM, Roland Huggins <[email protected]>
wrote:

> Just as a point of interest, ESFR can be used for OH.
>
>
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org <http://www.firesprinkler.org/>
>
>
>
>
>
> > On Mar 3, 2015, at 12:32 PM, Richard Mote <[email protected]>
> wrote:
> >
> > Building was originally bid as an ESFR, now the owner is coming back and
> saying it is going to be used for truck maintenance and wants OHII. We were
> going to try to use CMDA extended coverage OH and spread the spacing out a
> little. I am just trying to get up to speed, yesterday morning I was
> retired.
> >
> > Richard Mote CET
> > Rowe Sprinkler Systems, Inc.
>