All:
 
Seems pretty "black and white" to me - CPVC can be installed  in areas that 
do NOT require sprinkler protection in the  attic/interstitial areas...
 
Regards to All-
 
Jerry
[email protected]_ (mailto:[email protected]) 
 
Jerry D. Watts, SFPE
President & Co-Founder
ACCENT FIRE ENGINEERING INT'L. Ltd.*
Santa Fe, New Mexico USA
(800) 503.1961 nationwide
 
*Licensed Architects - Fire Protection  Engineers/Inspectors/Fire 
Investigators: AZ  CA  CO  NM   NV  NY  TX  UT  KS  MD  MS
 
 
 
In a message dated 5/20/2015 9:43:08 A.M. Mountain Daylight Time,  
[email protected] writes:

Agreed  Travis


Greg McGahan
Living Water Fire Protection, LLC  <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL  32533
850-937-1850
fax 850-937-1852

On Wed, May 20, 2015 at 10:41  AM, Travis Mack, SET <[email protected]>
wrote:

> A  general rule of thumb is you can run CPVC anywhere sprinklers are not
>  required.  If you want to run CPVC in an area where sprinklers  are
> required, you have to use sprinklers that are specially listed to  allow
> CPVC in those spaces.
>
> If you had an office  building that was framed in steel, then you could 
use
>  CPVC.
>
> Your case is very similar.  You want to run the  piping in a
> non-combustible area and supply pendent sprinklers in the  ceilings. I 
don't
> believe that violates any listings of the CPVC  piping.
>
> Travis Mack, SET
> MFP Design, LLC
> 2508  E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax:  866-430-6107
> email:[email protected]
>
>  http://www.mfpdesign.com
>  https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large  files to us via: https://www.hightail.com/u/MFPDesign
>
>
>  On 5/20/2015 8:38 AM, Sean Lockyer wrote:
>
>> I have an  interesting question to ask of everyone here. I am being asked
>> to  install an NFPA  13, non-residential sprinkler system in a small,  
new
>> building that will be constructed with wood. However, the wood  trusses 
will
>> consist of fire rated lumber with a flamespread  rating of less than 25,
>> which will not require sprinkler  protection since they would considered 
to
>> then be non-combustible,  or at the worst, limited combustible.
>>
>> With that being  said, could you then install CPVC piping in these
>> concealed areas  without also having to use the specially listed 
concealed
>>  sprinklers (such as the CC1, CC2, HIP, BB1, etc.) heads that Tyco makes 
 ?
>>
>> Remember, you can only install CPVC in an attic or a  combustible
>> concealed space if you also use those specially listed  heads but if the
>> area is technically not combustible I would say  that you could use CPVC
>> just like if you were using CPVC above an  gyp board ceiling in an office
>> for example - if you take the  listing literally.
>>
>> What does everyone else think  ?
>>
>>
>>             Sean Lockyer
>>           Project Designer              4617
>> Parkbreeze Court
>>         Cell    386-279-1197
>>  Orlando, Florida 32808
>>             [email protected]           Phone:
>> 407-816-9101
>>       www.AITLifeSafety.com       Fax:
>>  407-816-9104
>>
>>
>>  _______________________________________________
>> Sprinklerforum  mailing list
>>  [email protected]
>>
>>  
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>
>  _______________________________________________
> Sprinklerforum mailing  list
> [email protected]
>
>  
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum  mailing  list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to