yes and yes Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/>
> On Jun 19, 2015, at 10:52 AM, <[email protected]> <[email protected]> > wrote: > > Happy Friday Forumites > I'm looking for clarification/definition for intent in NFPA 13 12010 Edition > section 8.15.1.2.2 Concealed spaces of noncombustible and limited-combustible > construction with limited access and not permitting occupancy or storage of > combustibles shall not require sprinkler protection. > > First question - Does the space above the suspended ceiling of an office > occupancy, from the ceiling to the roof deck above meet the definition of > "concealed space"? > Second question- Does this same suspended ceiling (either acoustic tile or > sheetrock tile) meet the definition of "limited access"? > > Mark at Aero > 602 820-7894 > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org