That seems to be a common sense definition.
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
On 6/19/2015 11:32 AM, [email protected] wrote:
Would you say this description is correct? "Limited access" A space which is
not accessible by simply opening a door and walking into it. It can be accessed if
necessary, just not by the general public or employees at their normal work station.
Mark at Aero
602 820-7894
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On
Behalf Of Roland Huggins
Sent: Friday, June 19, 2015 11:18 AM
To: [email protected]
Subject: Re: Concealed Space Access definition
fundamentalist can be hard to deal with - lol.
The pont is that one could call it limited access but you are allowed to have
it (in other words, it does not have to be gypsum and being able to get to the
space is not a disqualifier - a bushism). The driver for omitting protection
is the area not used for storage (not used in the traditional warehouse sense)
or use as an occupied space.
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>
On Jun 19, 2015, at 11:06 AM, Steve Leyton <[email protected]> wrote:
FUNDAMENTALLY disagree (with all due respect). Accessible as in,
accessible for occupancy or storage? Or accessible as in, I can stick
my head up there. The latter does NOT require sprinkler protection,
which I think is the point of this query.
SML
-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Roland Huggins
Sent: Friday, June 19, 2015 11:05 AM
To: [email protected]
Subject: Re: Condealed Space Access definition
yes and yes
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>
On Jun 19, 2015, at 10:52 AM, <[email protected]>
<[email protected]> wrote:
Happy Friday Forumites
I'm looking for clarification/definition for intent in NFPA 13 12010
Edition section 8.15.1.2.2 Concealed spaces of noncombustible and
limited-combustible construction with limited access and not
permitting occupancy or storage of combustibles shall not require
sprinkler protection.
First question - Does the space above the suspended ceiling of an
office occupancy, from the ceiling to the roof deck above meet the
definition of "concealed space"?
Second question- Does this same suspended ceiling (either acoustic
tile or sheetrock tile) meet the definition of "limited access"?
Mark at Aero
602 820-7894
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org