Hello Forum,

Two weeks ago I said:

"I fixed it and compared the results for a wide range of flows to the
results in Roland's article and I will never bad-mouth Hazen, Williams, or
Roland again :)."

Here is a summary of the more exhaustive comparisons for the 2" and 2 1/2"
Main Drain scenarios:

https://www.dropbox.com/s/1tqp42gqdpxum04/BFP_Compare_Roland.pdf?dl=0

and here is the link to the issue of Roland's article:

http://digital.turn-page.com/i/127056-may-2013

I added (5) quantities to each calc:

1) velocity
2) HW pf/ft
3) DW pf/ft
4) HW va eq len
5) DW va eq len

Looking at 4) and 5) you might see why I said, "My concept of K-Value and Pf
and equivalent length being proportional to v^2 was exactly backwards."

I hope a Forumite or two finds this kind of thing as interesting as I do!!!

Thanks,

Brad Casterline