I wouldn't mind hearing this as well. I would think that between inspector's
test flows, 2" drain flows and annual backflow preventer tests (required by
states), that the health of the BFP would be sufficiently determined. Of course in Light/Ordinary Hazard situations, the 2" drain could discharge system demand, so the requirement would be met. Perhaps a full flow as part of an acceptance I could understand. Have there been any instances where there has been a backflow
preventer failure at full flow and not at a lower flow?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)
860-608-4559 (cell)
Sent using CloudMagic [https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
On Tue, Jun 23, 2015 at 1:55 AM, [email protected]
<[email protected]> wrote:
Something I have failed to understand, and would appreciate if someone can
enlighten me.

The forward flow test is required at the full system demand, presumably to check the operation of the BFP. If the test shows that the BFP will open at system demand, what guarantee is there that it will open at a lower flow. I would think higher the flow, greater the force and easier to open the check valves. Or am I
missing something?

Tony

----- Original Message -----

From: "Brad Casterline" <[email protected]>
To: [email protected]
Sent: Monday, June 22, 2015 10:42:17 AM
Subject: RE: BFP_Compare_Roland

Hello Forum,

Two weeks ago I said:

"I fixed it and compared the results for a wide range of flows to the
results in Roland's article and I will never bad-mouth Hazen, Williams, or
Roland again :)."

Here is a summary of the more exhaustive comparisons for the 2" and 2 1/2"
Main Drain scenarios:

https://www.dropbox.com/s/1tqp42gqdpxum04/BFP_Compare_Roland.pdf?dl=0

and here is the link to the issue of Roland's article:

http://digital.turn-page.com/i/127056-may-2013

I added (5) quantities to each calc:

1) velocity
2) HW pf/ft
3) DW pf/ft
4) HW va eq len
5) DW va eq len

Looking at 4) and 5) you might see why I said, "My concept of K-Value and Pf
and equivalent length being proportional to v^2 was exactly backwards."

I hope a Forumite or two finds this kind of thing as interesting as I do!!!

Thanks,

Brad Casterline
AFSA Designer Member and SET




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to