Hi Forum,

I am nearing the end of my obsession with this, at least posting about it.
To the spread sheet I had added the data for absolute roughness I found most
satisfying; there are four categories, each with minimum and maximum values.
Then I 'discovered' NFPA 750 (2015): 
Table 11.2.2(a) recommends a value for absolute roughness.
Table 11.2.2(b) shows approximate values for dynamic viscosity, and
densities for clean water.
The discussion in A.11.3 is very informative.
A.11.2.2 shows a formula for solving for the friction factor based on the
Reynold's number, velocity, and C-factor, but I rearranged it to solve for
the HW C-Factor instead due to the discussion in A.11.3. See G19 on the
spread sheet.

The utility of this is really to get a "Flow Test" at the riser gauge
without flowing any water. For example if the latest Main Drain tag says
Static = 52 PSI, Residual = ?? PSI, and you input the diameter, length and
fittings (column K), make sure the angle valve K-Value is correct for the
diameter at D7, and adjust the flow at B10 until you get 52 Pt (static at
riser) at G15, you will have a Static, Residual, and Flow with the riser
gauge as the Source Node.

Thanks,

Brad Casterline
AFSA Designer Member and SET