Here's the difference in the PVC versus chain issue.  

I could defend the chaining option based on the NFPA 13 standard since it is a 
viable alternative recognized by the fire sprinkler industry and established by 
the knowledge base of the authors of the NFPA Standards.  So while the Code 
states the valves are to be electronically supervised, this is a recognized 
option.

I could not defend using Shoe-Goo on PVC pipe because the AHJ said so if it 
wasn't documented as a viable option in any trade or industry standard or Code. 
 I'd have nothing to use as a defense for the choice.

Now per the IBC, there is language that grants permission to the code official 
to allow modifications to the code requirements based on unique conditions.  If 
the code official then uses an already established and accepted guideline such 
as NFPA 13 as a reason or source for his alternate direction and that decision 
complies with the directive as noted below, there is no dereliction.  
IBC 2012
[A] 104.10 Modifications. Wherever there are practical difficulties
involved in carrying out the provisions of this code,
the building official shall have the authority to grant modifications
for individual cases, upon application of the owner or
owner's representative, provided the building official shall
first find that special individual reason makes the strict letter
of this code impractical and the modification is in compliance
with the intent and purpose of this code and that such modification
does not lessen health, accessibility, life and fire
safety, or structural requirements. The details of action granting
modifications shall be recorded and entered in the files of
the department of building safety.

Good food for thought as we often get sucked into these "the AHJ said 
________________" issues where there is nothing more to stand on than that one 
person's opinion.  



Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Drucker
Sent: Tuesday, September 01, 2015 9:38 AM
To: [email protected]
Subject: RE: AHJ Powers

Members,

Someone's responsible.  Craig I agree with part of your thinking, if the 
sprinkler contractor was not responsible for the actual electrically supervised 
side of the equation, then mount the supervisory devices and so note in the 
final documentation making certain that the lack of electrical supervision is 
so noted.  Some sprinkler contractors go even further and provide a written 
quote to provide same and document an owners refusal therein making a 
reasonable attempt to fulfil the code requirements. Keep in mind that code 
officials are typically immune where there actions are not considered gross 
negligence, ie he/she made a mistake.  This immunity typically doesn't extend 
to other parties, I,e, the code official said it was ok that's my defense.  
That doesn't hold up as design professionals and contractors have a duty to 
comply.  For example if the code official said it was ok to use any kind of 
cement on cpvc would you ?

Food for thought.  As always the disclaimer.....the preceding is not a legal 
opinion, nor the opinion of the borough of red bank but merely an informal 
observation, always consult qualified legal council.


Gross Negligence

An indifference to, and a blatant violation of, a legal duty with respect to 
the rights of others.

Gross negligence is a conscious and voluntary disregard of the need to use 
reasonable care, which is likely to cause foreseeable grave injury or harm to 
persons, property, or both. It is conduct that is extreme when compared with 
ordinary Negligence, which is a mere failure to exercise reasonable care. 
Ordinary negligence and gross negligence differ in degree of inattention, while 
both differ from willful and wanton conduct, which is conduct that is 
reasonably considered to cause injury. This distinction is important, since 
contributory negligence-a lack of care by the plaintiff that combines with the 
defendant's conduct to cause the plaintiff's injury and completely bar his or 
her action-is not a defense to willful and wanton conduct but is a defense to 
gross negligence. In addition, a finding of willful and wanton misconduct 
usually supports a recovery of Punitive Damages, whereas gross negligence does 
not.

West's Encyclopedia of American Law, edition 2. Copyright 2008 The Gale Group, 
Inc. All rights reserved.


John Drucker
Assistant Construction Official
Fire Protection Subcode Official
Building/Fire/Electrical Inspector
Borough of Red Bank, NJ
90 Monmouth Street
Red Bank, New Jersey 07701
Cel/Text: 732-904-6823
Email: [email protected]




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Tuesday, September 01, 2015 9:22 AM
To: [email protected]
Subject: RE: AHJ Powers

What provides the electronic supervision, the fire alarm system.  Who provides 
the fire alarm system, the alarm or electrical contractor.  So as the fire 
sprinkler contractor if you provided and installed the supervisory switches why 
sweat this issue?  You provided your scope of work, it's up to another entity 
to connect and make it compliant.

If the AHJ ruled that chains were satisfactory are you as the sprinkler 
contractor going to petition the State for a ruling over him?

Is there a letter of acceptance?  If yes, move on unless you want to make this 
a Judge Judy episode.

Either way unless the alarm system is part of the sprinkler contractor scope, 
this is not a sprinkler contractor issue.  Why make it one?

Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Drucker
Sent: Tuesday, September 01, 2015 8:50 AM
To: [email protected]
Subject: RE: AHJ Powers

The requestor stipulated that the valves are required to be electrically 
supervised by applicable code, presumably the IBC.  Where conflict in code / 
standard occurs IBC trumps so NFPA-13 irrelevant.  Here's the code sections;

2009 IBC

102.4  Referenced Codes and Standards 

901.6 Supervisory Service

901.6.1 Automatic Sprinkler Systems

903.4 Sprinkler System Supervision and Alarms

903.4.1 Monitoring


If there's a loss these references may well be cited for the various parties to 
defend their actions with regards to a nationally recognized building code 
adopted by jurisdiction.

Hope that helps,

John Drucker
Assistant Construction Official
Fire Protection Subcode Official
Building/Fire/Electrical Inspector
Borough of Red Bank, NJ
90 Monmouth Street
Red Bank, New Jersey 07701
Cel/Text: 732-904-6823
Email: [email protected]










-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Tuesday, September 01, 2015 8:24 AM
To: [email protected]
Subject: RE: AHJ Powers

Yeah this is where the NFPA people need to be in-line with the ICC people.    
But the ICC also makes no exceptions for those installations where there is no 
alarm system to connect any signals.

Keep the documentation of the AHJ approval for posterity.  He signed off, he's 
the final say.  Move on to the next great adventure.

Round and round the mulberry bush.....................................


Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matthew J Willis
Sent: Tuesday, September 01, 2015 8:15 AM
To: [email protected]
Subject: RE: AHJ Powers

If the system is a Required system per IBC, then valves controlling water to 
sprinklers must be electrically supervised.

It is an IBC violation, not NFPA if I am assuming correctly.

R/
Matt

Matthew J. Willis
Project Manager
Rapid Fire Protection Inc.
1805 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Cell-605.391.2733
Fax:-605.348.0108



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Tuesday, September 01, 2015 6:12 AM
To: [email protected]
Subject: RE: AHJ Powers

NFPA 13 gives clear options, chaining and locking is one of them.  What's the 
issue here?  There are building installations where there is no requirement for 
a fire alarm system so there is no provision for supervising valves 
electronically, in those cases you chain or lock them.

8.16.1.1.2* Supervision.
8.16.1.1.2.1 Valves on connections to water supplies, sectional control and 
isolation valves, and other valves in supply pipes to sprinklers and other 
fixed water-based fire suppression systems shall be supervised by one of the 
following methods:
(1) Central station, proprietary, or remote station signaling service
(2) Local signaling service that will cause the sounding of an audible signal 
at a constantly attended point
(3) Valves locked in the correct position
(4) Valves located within fenced enclosures under the control of the owner, 
sealed in the open position, and inspected weekly as part of an approved 
procedure




Craig L. Prahl
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Monday, August 31, 2015 8:49 PM
To: [email protected]
Subject: AHJ Powers

What say you?
An inspector failed to require tamper switches on control valves. The job is 
complete and there are thousands of pounds of concrete between the control 
valves and the electrical panel. They placed a chain and lock and the chief 
declared the chain and lock meet intent...final approved. What say you?

Sent from my iPhone
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to