Why would you not want sprinkler protection in such a compartment?

SL



-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Jamie Seidl
Sent: Thursday, September 17, 2015 1:29 PM
To: [email protected]
Subject: Fuel fired furnace under stage

NFPA 13 2007 8.15.1.2.2 states that concealed spaces of noncombustible
and limited combustible construction with limited access and not
permitting occupancy or storage of combustibles shall not require
sprinkler protection.  The space shall be considered a concealed space
even with small openings such as those used as return air for a plenum.
Would this exception also work for an area below a noncombustible stage
housing a natural gas fired furnace?

Thanks Forum!