Why would you not want sprinkler protection in such a compartment?

SL



-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of Jamie Seidl
Sent: Thursday, September 17, 2015 1:29 PM
To: [email protected]
Subject: Fuel fired furnace under stage

NFPA 13 2007 8.15.1.2.2 states that concealed spaces of noncombustible and 
limited combustible construction with limited access and not permitting 
occupancy or storage of combustibles shall not require sprinkler protection.  
The space shall be considered a concealed space even with small openings such 
as those used as return air for a plenum.
Would this exception also work for an area below a noncombustible stage housing 
a natural gas fired furnace?

Thanks Forum!
Jamie Seidl