Someone has a lot of work to do.  Storage of this type of material goes far 
beyond just what kind of sprinkler system is in the building.  You are getting 
into significant building construction issues as the area you describe is most 
likely going to end up being an H-3 Hazardous occupancy if it's just consumer 
level fireworks.  [Table 307.1(1) IBC]

You definitely need to hire someone with Special Hazards Analysis experience 
not just some average commercial architect/engineer as once you venture into 
the world of special hazards there are a lot of things to analyze and 
investigate and coordinate between disciplines.   "H" occupancies touch all 
disciplines to some extent not just fire protection.

Also be looking at Section 307 of the Building code, Chapter 56 of the Fire 
Code along with NFPA 495 to get started. As you evaluate and substantiate the 
exact building occupancy category you will be led to other chapters or codes.  

First step would be to contact the local fire authority because some 
authorities may not even allow such a venue within their jurisdiction based on 
local building restrictions.   If they can't occupy the building all other 
investigations are moot.

Also see the info at the link provided, it appears that NFPA has withdrawn 1142 
due to some challenges to their procedures and such.
http://www.americanpyro.com/highlights---news-nfpa-withdraws-std--1124


Craig L. Prahl 
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Daniel Blanke
Sent: Friday, October 02, 2015 10:32 AM
To: [email protected]
Subject: Fireworks Storage

A customer has asked us to survey an existing sprinkler system in a 95,000 
square foot building to see if it is adequate for storage of consumer fireworks 
and alter the system accordingly. I don't see a single mention of the word 
fireworks in NFPA 13 and NFPA 1124 the Code for the Manufacture, 
Transportation, Storage, and Retail Sales of Fireworks and Pyrotechnic Articles 
leaves me with the impression that it is impossible to protect ​ ​ a building ​ 
​ with a water-based fire protection system that stores this type of product.
​ ​
We plan to involve an architect as well as the AHJ before moving forward.
​ ​
Does anyone have any experience with a similar situation?

Thanks.

Daniel Blanke | Owner & Founder
Capital Automatic Sprinkler, LLC
213 Mill Street
California, MO. 65018
Office: (573) 818-3052 ext. 700
Fax: (573) 818-3052
Cell: (573) 645-3251
www.capitalautomatic.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to