https://www.dropbox.com/s/7x6g8auwkgph2ho/PVC%20SPIGOT.pdf?dl=0
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
On 10/2/2015 9:46 AM, [email protected] wrote:
Pleas do.
Thank you,
Bob Knight
--- [email protected] wrote:
From: Richard Carr <[email protected]>
To: "[email protected]"
<[email protected]>
Subject: RE: PVC (C900) for spigot through floor
Date: Fri, 2 Oct 2015 16:42:55 +0000
Feb. 2014. I can send you a copy off line if you need.
Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville, Fl. 32205
[email protected]
904-781-8227
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On
Behalf Of [email protected]
Sent: Friday, October 02, 2015 12:39 PM
To: [email protected]
Subject: RE: PVC (C900) for spigot through floor
Thanks Richard, by any chance do you know what month and year that was?
Bob Knight
--- [email protected] wrote:
From: Richard Carr <[email protected]>
To: "[email protected]"
<[email protected]>
Subject: RE: PVC (C900) for spigot through floor
Date: Fri, 2 Oct 2015 16:33:47 +0000
YES, it is allowed. Article in Sprinkler Age by Phill Brown.
Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville, Fl. 32205
[email protected]
904-781-8227
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On
Behalf Of [email protected]
Sent: Friday, October 02, 2015 12:29 PM
To: [email protected]
Subject: PVC (C900) for spigot through floor
Good morning,
Is it permissible to install PVC (C900) as the spigot piece through the floor slab
of a building? There would be about 6 to 8" of exposed piping. All I can find
in the 2013 edition of 13 is that Fire Resistance of the Pipe shall be considered
(10.1.4 (1)).
It appears that this wording has been done away with in the 2016 edition and replaced
with this, "Where piping installed in a private fire service main must be installed
above grade, the piping materials shall conform to NFPA 13".
Based on this, it looks to me like using PVC through the floor will be
acceptable moving forward. Is this correct?
Thanks for the help,
Bob Knight, CET III
208-318-3057
www.firebyknight.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org