In the rewrite of NFPA 24 just completed, the following section was added:

   10.1.4.1 Underground piping shall be permitted to extend into the
   building through the slab or wall not more than 24 in. (0.6 m).

The circumstances you're describing were a part of that discussion.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/>

It should be noted that the above is my opinion as a member of the NFPA Installation of Private Fire Service Mains and their Appurtenances Committee in accordance with the NFPA Regulations Governing Committee Projects and should therefore not be considered, nor relied upon, as the official position of the NFPA or its Committees
***