The 65 psi end head pressure is a bitter pill but NFPA 13 allows them to be retained for modifications to existing systems. That clause is part of the current standard so bringing the system up to current standards does not exclude it’s application. Mediocre fire protection at best but allowed. A discussion with the AHJ at the BEGINNING beats a fight after the fact since interpretation enters the fray.
Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> > On Oct 2, 2015, at 12:41 PM, James Crawford <[email protected]> wrote: > > This is a sprinkler system that was designed to have in-rack sprinklers > installed at a future date if required, and for this tenant we were planning > on installing two levels of in-racks with a ceiling density of 0.45, this is > what is currently in this building. > > I see no need to change the roof system heads if they work. > > > > Thank you > > > James Crawford _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org