When using the EC-25 as a CMSA sprinkler (current spacing 10-5 X 13-5), the criteria for our application is 8 sprinklers at 40 psi. When calculating, do you calculate 4+4 or do you do 3+3+2? Tyco's data sheet does not give guidance, nor does NFPA 13, Chap 21.

I've been told use 1.2 * Sqrt (area). But is that the area based on max coverage of 14x14 (8*196 = 1568) or do you use area per sprinkler (140*8 = 1120).

The difference is that at 1568, my length down remote area is 48' which requires 4x2. The 1120 is 40. This is a weird configuration, so my heads are spaced at 13-5 on center. As such, that puts me at 3 sprinklers per line.

In this particular project, much of the piping is existing, and the difference is 17 psi between the 4+4 and 3+3+2. That difference requires removing existing 6" piping and replacing with existing 8" piping.

Does anyone have any guidance on this? My gut is that it is 4+4. My customer is saying it is 3+3+2.

--