In Virginia we use the 2010 edition

> From: [email protected]
> To: [email protected]
> Subject: RE: ESFR Sprinklers and covered catwalks
> Date: Fri, 30 Oct 2015 18:35:08 +0000
> 
> 2013 & 2016 editions no longer require calculating 2 additional ESFR's under 
> obstructions.
> 
> Peter Schwab
> VP of Purchasing and Engineering technologies
> 
> Wayne Automatic Fire Sprinklers Inc.
> 222 Capitol Court
> Ocoee, Fl 34761
> 
> Mobile: (407) 468-8248
> Direct: (407) 877-5570
> Fax: (407) 656-8026
> 
> www.waynefire.com
> 
> 
> 
> 
> 
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Mike Hairfield
> Sent: Friday, October 30, 2015 2:24 PM
> To: [email protected]
> Subject: RE: ESFR Sprinklers and covered catwalks
> 
> Put ESFR's under the catwalk and include two (2) additional ESFR's in the 
> calc's total of fourteen heads flowing.
> Just like it's an obstruction.
> 
> Mike
> 
> > From: [email protected]
> > To: [email protected]
> > Subject: RE: ESFR Sprinklers and covered catwalks
> > Date: Fri, 30 Oct 2015 18:16:25 +0000
> > 
> > The situation I was dealing with is not a rack.  It is a shelf - solid 
> > back, solid shelves, solid ends.  It is not likely to get a full scale test 
> > for a not-all-that-common setup.  Or maybe it is more common than I think.  
> > 
> > John F. Hoffman, PE*  \  Burns & McDonnell Senior Fire Protection 
> > Engineer O 816-349-6759 \  M 816-255-4102 [email protected]  \  
> > burnsmcd.com
> > 9400 Ward Parkway  \  Kansas City, MO 64114
> > 
> > Proud to be one of FORTUNE's 100 Best Companies to Work For Please 
> > consider the environment before printing this email.
> > *Registered in: MO
> > 
> > -----Original Message-----
> > From: Sprinklerforum 
> > [mailto:[email protected]] On Behalf Of 
> > Scott Futrell
> > Sent: Thursday, October 29, 2015 4:36 PM
> > To: [email protected]
> > Subject: RE: ESFR Sprinklers and covered catwalks
> > 
> > Hmmm...John that is interesting direction you are giving there.
> > 
> > Do you have NFPA 13 or full-scale testing to support the "ESFR could spray 
> > below the catwalk" comment? Or, that OH2 below the catwalk will not allow 
> > the fire to grow horizontally along the racking overwhelming the ESFR above?
> > 
> > If the catwalk doesn't extend through the rack how can you protect a 30' 
> > high (or pick a height) rack storage with QR sprinklers below the catwalk 
> > level and ESFR above the catwalk level when it's all the same rack storage 
> > from the ground up with flue spaces open and continuous to the roof.  I 
> > must be missing something here.
> > 
> > I assume the direction of the catwalk would/could enter into the scenario, 
> > but I would like to see your support for the comments you've made here, and 
> > if you have that support great!
> > 
> > Scott
> >  
> > Office: (763) 425-1001 x 2
> > Cell: (612) 759-5556
> > 
> > 
> > -----Original Message-----
> > From: Sprinklerforum 
> > [mailto:[email protected]] On Behalf Of 
> > John F Hoffman
> > Sent: Thursday, October 29, 2015 4:14 PM
> > To: [email protected]
> > Subject: RE: ESFR Sprinklers and covered catwalks
> > 
> > If the roof-level ESFR could spray below the catwalk (assuming open 
> > grating) you would not need the sprinklers under the catwalk.  But, as 
> > mentioned before, you are forced to put a cover on the grating so should be 
> > able to install whatever sprinklers can deal with the hazard under the 
> > grating.
> > 
> > Class IV shelf storage up to 12 feet high can be protected with OH2.   Even 
> > plastic shelf storage only requires EH1 or EH2 depending on height.   ESFR 
> > is overkill.  
> > 
> > John F. Hoffman, PE*  \  Burns & McDonnell Senior Fire Protection 
> > Engineer O 816-349-6759 \  M 816-255-4102 [email protected]  \  
> > burnsmcd.com
> > 9400 Ward Parkway  \  Kansas City, MO 64114
> > 
> > Proud to be one of FORTUNE's 100 Best Companies to Work For Please consider 
> > the environment before printing this email.
> > *Registered in: MO
> > 
> > 
> > 
> > 
> > 
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
>                                         
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]