It is my understanding that the ESFR's under the catwalk are needed to address 
commodity fires at the lower rack levels. Part of the effectiveness of the roof 
level ESFR's is their ability to spray the face of the products on the racks 
including those below the level of the catwalk. If SSU's are put down there it 
could greatly reduce the amount of water that reaches the lower storage levels.

I'm trying to find the source for that...

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 
 
913.888.0647 ph 
913.888.0618 f 
913.526.7443 cell 
www. AFPsprink.com 
 


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John F Hoffman
Sent: Thursday, October 29, 2015 3:39 PM
To: [email protected]
Subject: RE: ESFR Sprinklers and covered catwalks

We ran across this recently in an ESFR warehouse that has shelf storage with a 
grated walkway at about the 8 foot elevation.  Turns out they don't make an 
intermediate level ESFR or guards for them to meet 8.12.5.3.3.  So you are 
forced to put a solid walkway but the ESFR sprinklers with large pipe still 
extend down to where they can be damaged easily.  Seems logical to protect the 
area below the grating/covered walkway with quick response sprinklers for the 
hazard involved (non-ESFR) that can be equipped with guards and be SSUs.  
8.12.5.3.4 allows spray sprinklers for overhead doors. 

John F. Hoffman, PE*  \  Burns & McDonnell Senior Fire Protection Engineer O 
816-349-6759 \  M 816-255-4102 [email protected]  \  burnsmcd.com
9400 Ward Parkway  \  Kansas City, MO 64114

Proud to be one of FORTUNE's 100 Best Companies to Work For Please consider the 
environment before printing this email.
*Registered in: MO

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matthew J Willis
Sent: Thursday, October 29, 2015 10:39 AM
To: [email protected]
Subject: RE: ESFR Sprinklers and covered catwalks

I understand, but 8.12 is ESFR chapter.

R/
Matt

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Mackinnon
Sent: Thursday, October 29, 2015 9:37 AM
To: [email protected]
Subject: RE: ESFR Sprinklers and covered catwalks

Matt, we are not trying to omit sprinklers, just determine which sprinkler to 
use ESFR vs control mode...

Steven MacKinnon
Fire Protection Division
Hartcorn Plumbing and Heating, Inc.
850 South Second Street
Ronkonkoma, NY 11779
Office 631-580-2300  Fax - 631-580-1090



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matthew J Willis
Sent: Thursday, October 29, 2015 11:35 AM
To: [email protected]
Subject: RE: ESFR Sprinklers and covered catwalks

2007..

8.12.5.3 Continuous Obstructions Below the Sprinklers.
8.12.5.3.1 General Continuous Obstructions. Sprinklers shall be arranged with 
respect to obstructions in accordance with one of the following:
(1) Sprinklers shall be installed below continuous obstructions, or they shall 
be arranged to comply with Table 8.12.5.1.1 for horizontal obstructions 
entirely below the elevation of sprinklers that restrict sprinkler discharge 
pattern for two or more adjacent sprinklers such as ducts, lights, pipes, and 
conveyors.
(2) Additional sprinklers shall not be required where the obstruction is 2 in. 
(51 mm) or less in width and is located a minimum of 2 ft (0.6 m) below the 
elevation of the sprinkler deflector or is positioned a minimum of 1 ft (0.3 
m)horizontally from the sprinkler.
(3) Additional sprinklers shall not be required where the obstruction is 1 ft 
(0.3 m) or less in width and located a minimum of 1 ft (0.3 m) horizontally 
from the sprinkler.(4) Additional sprinklers shall not be required where the 
obstruction is 2 ft (0.6 m) or less in width and located a minimum of 2 ft (0.6 
m) horizontally from the sprinkler.(5) Ceiling sprinklers shall not be required 
to comply with Table 8.12.5.1.1 where a row of sprinklers is installed under 
the obstruction.


Where can you omit?

R/
Matt

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Mackinnon
Sent: Thursday, October 29, 2015 9:28 AM
To: [email protected]
Subject: RE: ESFR Sprinklers and covered catwalks

The conversation in the office kept going back to hvac ductwork and how you 
would place an ESFR sprinkler underneath when it became an obstruction... 
Normally there will be commodity stored under the duct, but in this situation, 
no stock will be in the catwalks, just the racks... so the additional ESFR 
sprinklers will spray the catwalks and not necessarily the commodity...  is 
this over kill??

Steven MacKinnon
Fire Protection Division
Hartcorn Plumbing and Heating, Inc.
850 South Second Street
Ronkonkoma, NY 11779
Office 631-580-2300  Fax - 631-580-1090



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Thursday, October 29, 2015 11:13 AM
To: [email protected]
Subject: RE: ESFR Sprinklers and covered catwalks

The catwalk is no different than any other obstruction within the area, right?  
For any other obstruction you would use the same ESFR's below the obstruction 
as you used at the ceiling/roof.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Mackinnon
Sent: Wednesday, October 28, 2015 3:45 PM
To: [email protected]
Subject: ESFR Sprinklers and covered catwalks

Hello everybody,

I have a situation where a client is looking to install an ESFR system 
protecting racks... they would like to add a solid floor catwalk system between 
the racks. Do you continue installing ESFR sprinklers under each level or can 
you install control mode sprinkler under the catwalks while the ESFR's at the 
ceiling protect the commodity?? 
I did look up the archives and a few people have asked similar questions over 
the years, but I don't see an answer... 
NFPA 13, 2007 ed. 

Thank you in advance!
Steven 



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to