I have seen it done in warehouse space when a tenant constructs offices below. The reason I was given from the AHJ is that if/when the office space is removed the warehouse is easily restored back to the original design criteria. Luckily we knew of this in advance and had a new low system included in our price.
Mike Hill -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Marc Walter, SET Sent: Tuesday, November 10, 2015 2:31 PM To: [email protected] Subject: Noncombustible concealed space I have a 1,300SF tenant finish project in a building that is post tension concrete. The tenant is dropping in a T-Bar grid ceiling throughout the space. I have the existing piping dropping new pendents to the ceiling and removing the uprights. The AHJ has rejected the plans based on the removal of the uprights citing 8.15.1.2.1 and 8.15.1.2.2 (NFPA 13:2013). His contention is that a T-Bar ceiling is a fully accessible space, and therefore requires sprinkler protection above. Anyone been hit with this before? Marc Walter, SET Sprinkler Design Services 780 6th Avenue Seaside, OR 97138 (503) 956-4019 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org