I have seen it done in warehouse space when a tenant constructs offices
below. The reason I was given from the AHJ is that if/when the office space
is removed the warehouse is easily restored back to the original design
criteria.
Luckily we knew of this in advance and had a new low system included in our
price.

Mike Hill


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Marc Walter, SET
Sent: Tuesday, November 10, 2015 2:31 PM
To: [email protected]
Subject: Noncombustible concealed space

I have a 1,300SF tenant finish project in a building that is post tension
concrete. The tenant is dropping in a T-Bar grid ceiling throughout the
space.

 

I have the existing piping dropping new pendents to the ceiling and removing
the uprights. The AHJ has rejected the plans based on the removal of the
uprights citing 8.15.1.2.1 and 8.15.1.2.2 (NFPA 13:2013).

 

His contention is that a T-Bar ceiling is a fully accessible space, and
therefore requires sprinkler protection above. Anyone been hit with this
before? 

 