You can also use Table 6.2.5.1 which indicates max. ceiling temps. It seems one should be able to justify the potential of greater than 100°F temperatures in a laundry room thus indicating an intermediate sprinkler should be installed as a safeguard...and still meet the standard.
Duane Johnson, PE Design Manager Strickland Fire Protection 5113 Berwyn Road College Park, MD 20740 301-474-1136 Office 301-455-0010 Cell -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Travis Mack, SET Sent: Thursday, November 12, 2015 11:12 AM To: [email protected] Subject: Re: Intermediate temperature sprinklers I thought it was that clear as well, but a large complex has been denied because of intermediate temp sprinklers in dwelling unit mechanical closets and laundry rooms. I just wanted to make sure I wasn't way off base on this. I am submitting an AFSA informal interpretation, as well as a technical question to NFPA to get the answer to provide to this plan reviewer as well. Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:[email protected] http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDesign On 11/12/2015 9:04 AM, Duane Johnson wrote: > How do you mess up: > > 8.3.2.1 Unless the requirements of 8.3.2.2, 8.3.2.3, 8.3.2.4, or 8.3.2.5 are > met, ordinary and intermediate-temperature sprinklers shall be used > throughout buildings. > > Intermediate can be used throughout unless other sections require a different > temperature rating. > > Duane Johnson, PE > Design Manager > Strickland Fire Protection > 5113 Berwyn Road > College Park, MD 20740 > 301-474-1136 Office > 301-455-0010 Cell > > > -----Original Message----- > From: Sprinklerforum > [mailto:[email protected]] On Behalf Of > Travis Mack, SET > Sent: Thursday, November 12, 2015 10:53 AM > To: [email protected] > Subject: Intermediate temperature sprinklers > > We are designing an apartment complex per NFPA 13 requirements. Is it > permissible to install intermediate temperature sprinklers throughout all > spaces (except those that would specifically require a high temp sprinkler > due to other sections)? > > The specific question arises because we have ordinary temperature sprinklers > throughout most areas, and intermediate temp sprinklers in mechanical closets > and laundry rooms in the dwelling units. The AHJ states that since the areas > (mech closets and laundry areas in the dwelling units) are conditioned > spaces, that we must use ordinary temperature rated sprinklers. He states > that Table 8.3.2.5(c) over-rides the flexibility provided by 8.3.2.1 which > allows ordinary or intermediate temp sprinklers throughout buildings. > > This has been common practice to install the intermediate temp sprinklers in > these areas. This is the first time that this plan reviewer has ever brought > this up. Some contractors in this area are moving toward intermediate temp > sprinklers throughout in residential areas for various reasons. > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org