You can also use Table 6.2.5.1 which indicates max. ceiling temps. It seems one 
should be able to justify the potential of greater than 100°F temperatures in a 
laundry room thus indicating an intermediate sprinkler should be installed as a 
safeguard...and still meet the standard.


Duane Johnson, PE
Design Manager
Strickland Fire Protection
5113 Berwyn Road
College Park, MD 20740
301-474-1136 Office
301-455-0010 Cell


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack, SET
Sent: Thursday, November 12, 2015 11:12 AM
To: [email protected]
Subject: Re: Intermediate temperature sprinklers

I thought it was that clear as well, but a large complex has been denied 
because of intermediate temp sprinklers in dwelling unit mechanical closets and 
laundry rooms.  I just wanted to make sure I wasn't way off base on this.

I am submitting an AFSA informal interpretation, as well as a technical 
question to NFPA to get the answer to provide to this plan reviewer as well.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 11/12/2015 9:04 AM, Duane Johnson wrote:
> How do you mess up:
>
> 8.3.2.1 Unless the requirements of 8.3.2.2, 8.3.2.3, 8.3.2.4, or 8.3.2.5 are 
> met, ordinary and intermediate-temperature sprinklers shall be used 
> throughout buildings.
>
> Intermediate can be used throughout unless other sections require a different 
> temperature rating.
>
> Duane Johnson, PE
> Design Manager
> Strickland Fire Protection
> 5113 Berwyn Road
> College Park, MD 20740
> 301-474-1136 Office
> 301-455-0010 Cell
>
>
> -----Original Message-----
> From: Sprinklerforum 
> [mailto:[email protected]] On Behalf Of 
> Travis Mack, SET
> Sent: Thursday, November 12, 2015 10:53 AM
> To: [email protected]
> Subject: Intermediate temperature sprinklers
>
> We are designing an apartment complex per NFPA 13 requirements.  Is it 
> permissible to install intermediate temperature sprinklers throughout all 
> spaces (except those that would specifically require a high temp sprinkler 
> due to other sections)?
>
> The specific question arises because we have ordinary temperature sprinklers 
> throughout most areas, and intermediate temp sprinklers in mechanical closets 
> and laundry rooms in the dwelling units.  The AHJ states that since the areas 
> (mech closets and laundry areas in the dwelling units) are conditioned 
> spaces, that we must use ordinary temperature rated sprinklers.  He states 
> that Table 8.3.2.5(c) over-rides the flexibility provided by 8.3.2.1 which 
> allows ordinary or intermediate temp sprinklers throughout buildings.
>
> This has been common practice to install the intermediate temp sprinklers in 
> these areas.  This is the first time that this plan reviewer has ever brought 
> this up.  Some contractors in this area are moving toward intermediate temp 
> sprinklers throughout in residential areas for various reasons.
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to