We used to have a guy in this area who would very specifically call out and
require a specific reason for anything other than an ordinary temperature
head.

It got me thinking, and now I just use standard everywhere.
I mean if you really think about it, something would have to be incredibly
wrong for a dwelling unit laundry room to get over 100° at the ceiling.
This is abnormal.
An outside closet with a hot water heater maybe I could see in certain
areas of the country, but I've been putting 155s in them for a while now.

For non-residential heads, 175s are a PITA to get sometimes as well.  They
never seem to be in stock when you need them.  I just go to 200s for those
and call it a day.


Benjamin Young

On Thu, Nov 12, 2015 at 1:11 PM, Travis Mack, SET <[email protected]>
wrote:

> I tried.  The response is that we are required to use the table, and that
> governs everything.  However, the contractor does not want ordinary temp
> sprinklers in this area.  So, I am having to track down some
> interpretations and such that prove the point.
>
> Gotta love the games we have to play.
>
> I will say that this reviewer is normally very good and quite nice to work
> with.  Something must have recently happened to cause him to flag this as
> an issue.
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
>
> http://www.mfpdesign.com
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
>
> On 11/12/2015 11:07 AM, Ed Kramer wrote:
>
>> So ask him where in the table (or the text) it say if you're more than the
>> minimum distance away for the ordinary temp sprink that you must use an
>> ordinary temp sprink?  He's really reaching.
>>
>> Ed Kramer
>> Lawrence, KS
>> -----Original Message-----
>> From: Sprinklerforum [mailto:
>> [email protected]]
>> On Behalf Of Travis Mack, SET
>> Sent: Thursday, November 12, 2015 11:39 AM
>> To: [email protected]
>> Subject: Re: Intermediate temperature sprinklers
>>
>> For example, the plan reviewer is stating that if the sprinkler is >6"
>> from a furnace or water heater, it MUST be ordinary temp rated.
>>
>> I understand the standard to state that you can use intermediate or
>> ordinary
>> throughout.  Table 8.3.2.5(c) just states that if I am within certain
>> distances to a heat source, I MUST use the intermediate temp sprinkler.
>>
>> The plan reviewer is reading that if I am more than the minimum distance
>> away, I MUST use ordinary.  He is stating that Table 8.3.2.5(c) over-rides
>> 8.3.2.1.
>>
>> So, who is correct?  That is the question that I need to be able to
>> resolve
>> with the plan reviewer.
>>
>> Travis Mack, SET
>> MFP Design, LLC
>> 2508 E Lodgepole Drive
>> Gilbert, AZ 85298
>> 480-505-9271
>> fax: 866-430-6107
>> email:[email protected]
>>
>> http://www.mfpdesign.com
>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>
>> On 11/12/2015 10:29 AM, Ed Kramer wrote:
>>
>>> Table 8.3.2.5(c) gives the minimum distance from various heat sources
>>> for both ordinary and intermediate temp sprinks.  I don't see anything
>>> in that table that dictates which sprink temp must be used.  Are we
>>> missing something?
>>>
>>> Ed Kramer
>>> Lawrence, KS
>>>
>>> -----Original Message-----
>>> From: Sprinklerforum
>>> [mailto:[email protected]]
>>> On Behalf Of Travis Mack, SET
>>> Sent: Thursday, November 12, 2015 9:53 AM
>>> To: [email protected]
>>> Subject: Intermediate temperature sprinklers
>>>
>>> We are designing an apartment complex per NFPA 13 requirements.  Is it
>>> permissible to install intermediate temperature sprinklers throughout
>>> all spaces (except those that would specifically require a high temp
>>> sprinkler due to other sections)?
>>>
>>> The specific question arises because we have ordinary temperature
>>> sprinklers throughout most areas, and intermediate temp sprinklers in
>>> mechanical closets and laundry rooms in the dwelling units.  The AHJ
>>> states that since the areas (mech closets and laundry areas in the
>>> dwelling units) are conditioned spaces, that we must use ordinary
>>>
>> temperature rated sprinklers.
>>
>>> He states that Table 8.3.2.5(c) over-rides the flexibility provided by
>>> 8.3.2.1 which allows ordinary or intermediate temp sprinklers
>>> throughout buildings.
>>>
>>> This has been common practice to install the intermediate temp
>>> sprinklers in these areas.  This is the first time that this plan
>>> reviewer has ever brought this up.  Some contractors in this area are
>>> moving toward intermediate temp sprinklers throughout in residential
>>> areas for various reasons.
>>>
>>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to