1) There is no 2015 edition of NFPA 14.  The 2016 has been final-drafter, and I 
don't believe there were any NITMAM's so adoption is imminent if I'm not 
mistaken.

2) Jerry - as for viewing the changes, you can see the First Draft and Second 
Draft reports on line at nfpa.org.   Section 7.3.2 Locations of Hose 
Connections has been overhauled.   The committee used its Imperial powers to 
combine four PI's into a single revision of that chapter, including some 
committee comments and, in the 2nd Draft cycle, the work product of a task 
group on 2-hour separations.   It will be twice as long and much more specific.

3) To the issue of the valve that is shown in Fig. A.7.3.2(5), it's my personal 
opinion that the valve is not required (nor desirable) in an environment that 
is NOT subject to freezing.   

Just sayin ...

The foregoing is my opinion only and does not necessarily represent the opinion 
or intent of the NFPA 14 Technical Committee on Standpipe and Hose Systems.

Steve Leyton
Protection Design & Consulting
San Diego, CA



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jerry Van Kolken
Sent: Monday, November 23, 2015 10:35 AM
To: [email protected]
Subject: RE: Class 1 Standpipe Roof Valve

Norman,

Is there any where I can view these changes?

Jerry Van Kolken
Millennium Fire Protection
(760) 722-2722

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Norman Arendt
Sent: Monday, September 28, 2015 4:30 PM
To: [email protected]
Subject: Re: Class 1 Standpipe Roof Valve

2015 code removes this requirement.

----- Original Message -----
From: Jerry Van Kolken <[email protected]>
To: [email protected]
Sent: Mon, 28 Sep 2015 18:44:58 -0400 (EDT)
Subject: Class 1 Standpipe Roof Valve

According to the NFPA 14-A.7.3.2(5) (13Ed.) There is gate valve installed 
isolating the hose valve on the roof.  Is there verbiage about this isolation 
valve? Is the valve required if you're not in areas subject to freezing? 

 

Jerry Van Kolken

Millennium Fire Protection Corp.

101 Copperwood Way, Suite H

Oceanside, CA 92058

(760) 722-2722 FX 722-2730

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

--
Norman Arendt, PhD, CFII, CMAS
Middleton Fire District Plan Reviewer and Investigator Board Member ASSE/ASIS 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to