1) There is no 2015 edition of NFPA 14. The 2016 has been final-drafter, and I don't believe there were any NITMAM's so adoption is imminent if I'm not mistaken.
2) Jerry - as for viewing the changes, you can see the First Draft and Second Draft reports on line at nfpa.org. Section 7.3.2 Locations of Hose Connections has been overhauled. The committee used its Imperial powers to combine four PI's into a single revision of that chapter, including some committee comments and, in the 2nd Draft cycle, the work product of a task group on 2-hour separations. It will be twice as long and much more specific. 3) To the issue of the valve that is shown in Fig. A.7.3.2(5), it's my personal opinion that the valve is not required (nor desirable) in an environment that is NOT subject to freezing. Just sayin ... The foregoing is my opinion only and does not necessarily represent the opinion or intent of the NFPA 14 Technical Committee on Standpipe and Hose Systems. Steve Leyton Protection Design & Consulting San Diego, CA -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Jerry Van Kolken Sent: Monday, November 23, 2015 10:35 AM To: [email protected] Subject: RE: Class 1 Standpipe Roof Valve Norman, Is there any where I can view these changes? Jerry Van Kolken Millennium Fire Protection (760) 722-2722 -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Norman Arendt Sent: Monday, September 28, 2015 4:30 PM To: [email protected] Subject: Re: Class 1 Standpipe Roof Valve 2015 code removes this requirement. ----- Original Message ----- From: Jerry Van Kolken <[email protected]> To: [email protected] Sent: Mon, 28 Sep 2015 18:44:58 -0400 (EDT) Subject: Class 1 Standpipe Roof Valve According to the NFPA 14-A.7.3.2(5) (13Ed.) There is gate valve installed isolating the hose valve on the roof. Is there verbiage about this isolation valve? Is the valve required if you're not in areas subject to freezing? Jerry Van Kolken Millennium Fire Protection Corp. 101 Copperwood Way, Suite H Oceanside, CA 92058 (760) 722-2722 FX 722-2730 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org -- Norman Arendt, PhD, CFII, CMAS Middleton Fire District Plan Reviewer and Investigator Board Member ASSE/ASIS _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org