Ask the plan reviewer why they want it, besides the fact that it's "in the 
picture".   What's the benefit if it's normally closed and has to be opened by 
fire-fighters prior to using the roof outlets or testing the standpipe?  
Especially if the roof connection is fitted with normally closed valves. 

The draft reports may help illustrate that the committee's intent is that the 
valve is only required in areas subject to freezing.

SML





-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jerry Van Kolken
Sent: Monday, November 23, 2015 11:22 AM
To: [email protected]
Subject: RE: Class 1 Standpipe Roof Valve

Thanks for pointing me to the Drafts.

I'm trying to get away from having to install the valve, but the reviewer wants 
it to match the picture.

Jerry Van Kolken
Millennium Fire Protection
(760) 722-2722


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Steve Leyton
Sent: Monday, November 23, 2015 11:03 AM
To: [email protected]
Subject: RE: Class 1 Standpipe Roof Valve

1) There is no 2015 edition of NFPA 14.  The 2016 has been final-drafter, and I 
don't believe there were any NITMAM's so adoption is imminent if I'm not 
mistaken.

2) Jerry - as for viewing the changes, you can see the First Draft and
Second Draft reports on line at nfpa.org.   Section 7.3.2 Locations of Hose
Connections has been overhauled.   The committee used its Imperial powers to
combine four PI's into a single revision of that chapter, including some 
committee comments and, in the 2nd Draft cycle, the work product of a task
group on 2-hour separations.   It will be twice as long and much more
specific.

3) To the issue of the valve that is shown in Fig. A.7.3.2(5), it's my personal 
opinion that the valve is not required (nor desirable) in an
environment that is NOT subject to freezing.   

Just sayin ...

The foregoing is my opinion only and does not necessarily represent the opinion 
or intent of the NFPA 14 Technical Committee on Standpipe and Hose Systems.

Steve Leyton
Protection Design & Consulting
San Diego, CA



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Jerry Van Kolken
Sent: Monday, November 23, 2015 10:35 AM
To: [email protected]
Subject: RE: Class 1 Standpipe Roof Valve

Norman,

Is there any where I can view these changes?

Jerry Van Kolken
Millennium Fire Protection
(760) 722-2722

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Norman Arendt
Sent: Monday, September 28, 2015 4:30 PM
To: [email protected]
Subject: Re: Class 1 Standpipe Roof Valve

2015 code removes this requirement.

----- Original Message -----
From: Jerry Van Kolken <[email protected]>
To: [email protected]
Sent: Mon, 28 Sep 2015 18:44:58 -0400 (EDT)
Subject: Class 1 Standpipe Roof Valve

According to the NFPA 14-A.7.3.2(5) (13Ed.) There is gate valve installed 
isolating the hose valve on the roof.  Is there verbiage about this isolation 
valve? Is the valve required if you're not in areas subject to freezing? 

 

Jerry Van Kolken

Millennium Fire Protection Corp.

101 Copperwood Way, Suite H

Oceanside, CA 92058

(760) 722-2722 FX 722-2730

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

--
Norman Arendt, PhD, CFII, CMAS
Middleton Fire District Plan Reviewer and Investigator Board Member ASSE/ASIS 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________