Sorry, baffle was wrong term to use. SD heads can't be installed floating out in space like that, they have to be so many inches away from a draft curtain or shear wall, kind of like sidewalls.
If you call tech support and/or watch the attic head webinar on the Tyco tech exchange website, it will cover this. They are somewhat defacto baffles as well since the maximum 5ft spacing of the AP from the edge of the slope means you are hard pressed to maintain the required 7ft clearance between them and the SDs. Stick with figure 20-B-3 and you can never go wrong with attic heads. On Tuesday, January 26, 2016, Brian Harris <[email protected]> wrote: > Ben- > I don't see on the data sheet where it requires baffles on the back side > of the SD heads, can you point me in the right direction? > > Brian Harris, CET > BVS Systems Inc. > bvssytemsinc.com > > > -----Original Message----- > From: Sprinklerforum [mailto: > [email protected] <javascript:;>] On Behalf > Of Ben Young > Sent: Tuesday, January 26, 2016 12:56 PM > To: [email protected] <javascript:;> > Subject: Re: Attic Heads > > Avoid HIPs and SDs like the plague. > If you go down the sides of the hip with SDs and then backfill with APs > you have to install baffles on the backside of the SD. > > Your best bet is just to always use APs across the entire hip area, > especially with the new hip rule added to the 2016 edition of NFPA 13. > Hopefully this will eventually get added to the attic head datasheet. > > I got suckered into using SDs on an offset and it was a nightmare. But > yeah, HIPs are basically no good anymore. I haven't used any in about 12 > years and for some reason I design a lot of attic systems... > > > Benjamin Young > > On Tue, Jan 26, 2016 at 9:14 AM, Brian Harris <[email protected] > <javascript:;>> > wrote: > > > I'm working on an attic system using the Tyco attic heads and was > > wondering if it's "normal" to use SD heads from the Ridge halfway down > > the Hip and then use the HIP sprinklers starting where the trusses run > > perpendicular to the outside wall? I don't do a whole lot of wood > > buildings and this is the first time I've seen the trusses change > > direction half way down the Hip instead of at the Ridge, not really an > > example of it in the Tyco data sheets. > > > > Brian Harris, CET > > BVS Systems Inc. > > Sprinkler Division > > bvssystemsinc.com<http://bvssystemsinc.com/> > > Phone: 704.896.9989 > > Fax: 704.896.1935 > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] <javascript:;> > > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > > er.org > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] <javascript:;> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] <javascript:;> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > -- Benjamin Young _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org