Unless the water purveyor or local ordinance has a 20 psi minimum requirement, 
there's no reason they'd have to provide a safeguard.  It's a common limit, but 
it's a rule of thumb unless codified as it's not in most of the common building 
codes and standards.  That said, if they have pressure to spare, a low suction 
control valve would be the way to go if you want or need to maintain 20 PSI or 
more for safety and have room to repipe the discharge side (and pick up a 
sensing line on the suction side).

Mike Morey, CFPS, SET
Planner Scheduler/Designer
BMWC Constructors, Inc.
1740 W. Michigan St, Indianapolis, IN 46222
O: 317.651.0596 | C: 317.586.8111
mo...@bmwc.com | www.bmwc.com

________________________________________
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> on behalf 
of Todd Williams <fpdcdes...@gmail.com>
Sent: Tuesday, February 16, 2016 7:41 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Oversized fire pump

I am working on a facility with a fire pump that was oversized for the
available
public water supply. The pump is 1500 gpm at 85 psi. At 1500 gpm, the
suction
pressure drops to 18 psi. This is characteristic of the water supply and is
not
due to a shut valve or other obstruction. The pump was installed in 2009.
Are
there any safeguards that I should recommend for this situation?

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to