My concern is that the 18 psi suction pressure occurs at rated flow. Since the
pump has the capacity to flow at 150%, is there a danger of dropping the suction
pressure dangerously low. The building is a hospital.

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic 
[https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
On Tue, Feb 16, 2016 at 7:52 AM, Richard Carr <rc...@coxfire.com> wrote:
If you maintaining 18 psi on the suction side with the pump running, why would
you do anything?

Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville, Fl. 32205
rc...@coxfire.com
904-781-8227

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Matt Grise
Sent: Tuesday, February 16, 2016 7:42 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Oversized fire pump

How about a suction control valve?

Matt Grisé PE*, LEED AP, NICET II
Sales Engineer
Alliance Fire Protection
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO

913.888.0647 ph
913.888.0618 f
913.526.7443 cell
www. AFPsprink.com



-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Todd Williams
Sent: Tuesday, February 16, 2016 6:41 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Oversized fire pump

I am working on a facility with a fire pump that was oversized for the available
public water supply. The pump is 1500 gpm at 85 psi. At 1500 gpm, the suction
pressure drops to 18 psi. This is characteristic of the water supply and is not
due to a shut valve or other obstruction. The pump was installed in 2009.
Are
there any safeguards that I should recommend for this situation?

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to