It sounds like the 1,000 gpm standpipe demand is the worst case. If so, you 
should be fine and there should be instructions/signage provided at the pump 
about limiting flows during pump tests. Looks like a Mechanical Engineer was 
involved in replacing the previous pump; or a contractor talked someone into a 
bigger sale (or both).

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Todd Williams
Sent: Tuesday, February 16, 2016 8:12 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Oversized fire pump

Meeting demand is not an issue for sprinklers. Not sure about standpipes but 
demand Dow would be no more than 1000 gpm.
Interesting side note: this pump replaced a 1000 gpm at 100 psi which would 
have worked fine with the water. Anecdotally, this pump was upsize because it 
was needed for the new 2 story cancer treatment center(?)

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 
860-535-2080 (ofc) 860-608-4559 (cell) Sent using CloudMagic 
[https://cloudmagic.com/k/d/mailapp?ct=pi&cv=6.0.64&pv=8.2]
On Tue, Feb 16, 2016 at 9:04 AM, Richard Carr <rc...@coxfire.com> wrote:
You can flow 126% of rated capacity, may not be a problem if you are meeting 
your system demand.

Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville, Fl. 32205
rc...@coxfire.com
904-781-8227


-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Richard Carr
Sent: Tuesday, February 16, 2016 8:56 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Oversized fire pump

Do you know what the system demand is?

Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville, Fl. 32205
rc...@coxfire.com
904-781-8227


-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Todd Williams
Sent: Tuesday, February 16, 2016 8:39 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Oversized fire pump

The water supply goes to 0 at roughly 1900 gpm

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell) Sent using CloudMagic 
[https://cloudmagic.com/k/d/mailapp?ct=pi&cv=6.0.64&pv=8.2]
On Tue, Feb 16, 2016 at 7:58 AM, Michael Hill <mi...@phoenixfp.net> wrote:
Do you have positive pressure when testing for 150% capacity?


Mike Hill

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Matt Grise
Sent: Tuesday, February 16, 2016 7:57 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Oversized fire pump

That might be a little too low pressure for the water company.

Matt Grisé PE*, LEED AP, NICET II
Sales Engineer
Alliance Fire Protection
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO

913.888.0647 ph
913.888.0618 f
913.526.7443 cell
www. AFPsprink.com



-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Richard Carr
Sent: Tuesday, February 16, 2016 6:52 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Oversized fire pump

If you maintaining 18 psi on the suction side with the pump running, why would 
you do anything?

Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville, Fl. 32205
rc...@coxfire.com
904-781-8227

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Matt Grise
Sent: Tuesday, February 16, 2016 7:42 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Oversized fire pump

How about a suction control valve?

Matt Grisé PE*, LEED AP, NICET II
Sales Engineer
Alliance Fire Protection
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO

913.888.0647 ph
913.888.0618 f
913.526.7443 cell
www. AFPsprink.com



-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Todd Williams
Sent: Tuesday, February 16, 2016 6:41 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Oversized fire pump

I am working on a facility with a fire pump that was oversized for the 
available public water supply. The pump is 1500 gpm at 85 psi. At 1500 gpm, the 
suction pressure drops to 18 psi. This is characteristic of the water supply 
and is not due to a shut valve or other obstruction. The pump was installed in 
2009.
Are
there any safeguards that I should recommend for this situation?

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to