2015 IRC/NJ Edition Section R-300  (The new code language which now
recognizes 13D and P2904 for Height and Area)

SECTION R300
HEIGHT AND AREA LIMITATIONS

Buildings of Type VB, unprotected wood framed construction,
as that term is defined in Section 602 of the building
subcode, shall be not more than two stories, not more than 35
feet in height, and not more than 4,800 square feet in area per
floor. For the purpose of applying this section, a habitable
attic shall not constitute a story.

R300.1 Increases in Height. The building shall be not more
than three stories and not more than 55 feet in height where
the building is equipped throughout with an automatic sprinkler
system installed in accordance with the National Fire
Protection Association (NFPA) Standard 13D or Section
P2904.

R300.2 Increases in area. The area of a building may be
increased as provided in Sections R300.2.1 and R300.2.2
below.

R300.2.1 The area limitation shall be unlimited where a
building is equipped throughout with an automatic sprinkler
system installed in accordance with NFPA Standard
13D or Section P2904.

R300.2.2 The area limitation shall be permitted to be
increased two percent for each one percent of excess frontage
where a building has more than 25 percent of the
building perimeter fronting on a street or other unoccupied
space. The unoccupied space shall be on the same lot or
dedicated for public use, shall be not less than 30 feet in
width, and shall have access from a street by a posted fire
lane that is not less than 18 feet in width.

R300.3 Buildings of VA construction. Buildings of VA,
protected wood-framed construction, as that term is defined
in Section 602 of the building subcode, shall be not more than
three stories, not more than 40 feet in height, and not more
than 10,200 square feet in area per floor.

R300.3.1 Buildings of VA construction greater than three
stories in height shall be designed and constructed in
accordance with the building subcode.

R300.3.2 Buildings of VA construction shall be permitted
to be increased in area in accordance with R300.2.

R300.4 Buildings of other types of construction. The
height and area limits allowable for buildings of construction
type VA shall apply to other construction types, as they are
defined in Section 602 of the building subcode, provided that
the fire ratings of building elements meet or exceed the
requirements for type VA in Tables 601 and 602 of the building
subcode.



John Drucker, CET
Assistant Construction Official
Fire Protection Subcode Official
Building/Fire/Electrical Inspector
Borough of Red Bank
Red Bank, New Jersey
Email: [email protected]
Cell/Text: 732-904-6823




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to