Ron,

Nope, it’s designed that way. I’ve asked fitters to look, and I’ve looked at 
new ones off the truck. That’s the way it comes. Data sheet doesn’t show it, or 
say anything about it.

Nope.

I’m thinking most don’t realize this, and most don’t realize wiping off the 
seat pushes the gunk into the slot that leads to the two holes.

Scott

Office: (763) 425-1001 x 202
Cell: (612) 759-5556

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of rongreenman .
Sent: Tuesday, May 17, 2016 8:31 PM
To: [email protected]
Subject: Re: Tyco Dry Pipe Valve

Maybe just a bad casting. Nothing about that in the cut sheet and that would be 
some neon flashing sign if there was a special tee in the alarm line.

Have you talked to Tyco?

As an example of this Viking has special ball drips that work only on 
designated valve trims. One that will not work with a DPV may be for a deluge 
valve.The info for this is glaring when you actually go looking for it. 