I have installed a test header on a riser to do a flow test of a backflow,
take a look at NFPA #13 2010 10.10.2.5
Ryan Labrie
Fire Protection Designer
Critical System Solutions, LLC
2830 Scherer Drive, Suite 300
St. Petersburg, FL 33716
Office: 727.209.5122
Fax: 727.209.5126
Cell: 813.394.3978
Email: rlab...@criticalsystemsolutions.com
[rlab...@criticalsystemsolutions.com]
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
Michael Hill
Sent: Thursday, July 14, 2016 8:55 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Test header on riser
Have not heard of this before. Perhaps he wants to do forward flow test for
backflow preventer?
Mike Hill
From: Sprinklerforum [
mailto:sprinklerforum-boun...@lists.firesprinkler.org
[sprinklerforum-boun...@lists.firesprinkler.org] ] On Behalf Of Todd
Williams
Sent: Thursday, July 14, 2016 8:41 AM
To: sprinklerforum@lists.firesprinkler.org
[sprinklerforum@lists.firesprinkler.org]
Subject: Test header on riser
Is there any requirement to install a test header on a riser without a pump
(In addition to arrangement for full flow FDC test)? I have an engineer
insisting that it is. When I asked for referenced, I get the "you look it
up" response. Just want to be sure before I scream back
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]_______________________________________________