As an engineer who just issued a design with such a test header (COE project 
where they "suggested" we look at this provision in the design). My view is 
that the FDC is fine for project with less than 500 gpm flow requirements. If 
over that (and in my case the flow was 1100 gpm), then we need a test header so 
we can properly demonstrate the flow rate.

David Toshio Williams, FPE, LEED-AP O+M
(218) 279-2436 direct | (218) 310-2446 cell
LHB, Inc. | PERFORMANCE DRIVEN DESIGN



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Todd Williams
Sent: Thursday, July 14, 2016 8:16 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Test header on riser

We installed a by-pass on the FDC line for the forward flow test, but he wants 
a test header as well.
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-608-4559 (cell)

Sent using CloudMagic<https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2>

On Thu, Jul 14, 2016 at 8:58 AM, Ryan Labrie 
<rlab...@criticalsystemsolutions.com<mailto:rlab...@criticalsystemsolutions.com>>
 wrote:
I have installed a test header on a riser to do a flow test of a backflow, take 
a look at NFPA #13 2010 10.10.2.5

Ryan Labrie
Fire Protection Designer

Critical System Solutions, LLC
2830 Scherer Drive, Suite 300
St. Petersburg, FL  33716
Office: 727.209.5122
Fax:      727.209.5126
Cell:     813.394.3978
Email:  
rlab...@criticalsystemsolutions.com<mailto:rlab...@criticalsystemsolutions.com>

[CSS Logo]

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Michael Hill
Sent: Thursday, July 14, 2016 8:55 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Test header on riser

Have not heard of this before. Perhaps he wants to do forward flow test for 
backflow preventer?

Mike Hill

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Todd Williams
Sent: Thursday, July 14, 2016 8:41 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Test header on riser

Is there any requirement to install a test header on a riser without a pump (In 
addition to arrangement for full flow FDC test)? I have an engineer insisting 
that it is. When I asked for referenced, I get the "you look it up" response. 
Just want to be sure before I scream back
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-608-4559 (cell)

Sent using CloudMagic<https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2>