Why do you need to demonstrate the flow rate? The purpose of the forward
flow test is to fully operate the back flow valve. A flow at 500 GPM will
not open the valve fully?

On Jul 14, 2016 9:52 AM, "David Williams" <david.willi...@lhbcorp.com>
wrote:

> As an engineer who just issued a design with such a test header (COE
> project where they “suggested” we look at this provision in the design). My
> view is that the FDC is fine for project with less than 500 gpm flow
> requirements. If over that (and in my case the flow was 1100 gpm), then we
> need a test header so we can properly demonstrate the flow rate.
>
>
>
> *David Toshio Williams, FPE, LEED-AP O+M*
>
> *(218) 279-2436 <%28218%29%20279-2436> direct | (218) 310-2446
> <%28218%29%20310-2446> cell        *
>
> *LHB, Inc. | PERFORMANCE **DRIVEN **DESIGN*
>
>
>
>
>
> *From:* Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Todd
> Williams
> *Sent:* Thursday, July 14, 2016 8:16 AM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* RE: Test header on riser
>
>
>
> We installed a by-pass on the FDC line for the forward flow test, but he
> wants a test header as well.
>
> Todd G Williams, PE
>
> Fire Protection Design/Consulting
>
> Stonington, CT
>
> 860-535-2080 (ofc)
>
> 860-608-4559 (cell)
>
>
>
> Sent using CloudMagic
> <https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2>
>
>
>
> On Thu, Jul 14, 2016 at 8:58 AM, Ryan Labrie <
> rlab...@criticalsystemsolutions.com> wrote:
>
> I have installed a test header on a riser to do a flow test of a backflow,
> take a look at NFPA #13 2010 10.10.2.5
>
>
>
> *Ryan Labrie*
>
> Fire Protection Designer
>
>
>
>
> *Critical System Solutions, LLC *2830 Scherer Drive, Suite 300
> St. Petersburg, FL  33716
> Office: 727.209.5122
>
> Fax:      727.209.5126
>
> Cell:     813.394.3978
>
> Email:  rlab...@criticalsystemsolutions.com
>
>
>
> [image: CSS Logo]
>
>
>
> *From:* Sprinklerforum [
> mailto:sprinklerforum-boun...@lists.firesprinkler.org
> <sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *Michael
> Hill
> *Sent:* Thursday, July 14, 2016 8:55 AM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* RE: Test header on riser
>
>
>
> Have not heard of this before. Perhaps he wants to do forward flow test
> for backflow preventer?
>
>
>
> Mike Hill
>
>
>
> *From:* Sprinklerforum [
> mailto:sprinklerforum-boun...@lists.firesprinkler.org
> <sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *Todd
> Williams
> *Sent:* Thursday, July 14, 2016 8:41 AM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* Test header on riser
>
>
>
> Is there any requirement to install a test header on a riser without a
> pump (In addition to arrangement for full flow FDC test)? I have an
> engineer insisting that it is. When I asked for referenced, I get the "you
> look it up" response. Just want to be sure before I scream back
>
> Todd G Williams, PE
>
> Fire Protection Design/Consulting
>
> Stonington, CT
>
> 860-535-2080 (ofc)
>
> 860-608-4559 (cell)
>
>
>
> Sent using CloudMagic
> <https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>