In the case I mentioned, the local FD agreed with me that creating a two-zone 
system for 15 PSI was of no value when all of the components were not just 
rated but listed for the working pressure.  I’m a big proponent of keeping it 
as simple as possible.  Why would I want to use two pumps (or complements of 
pumps if redundancy is required) when I can use one?   Why create two zones 
(including a second complement of FDC’s) if I don’t have to?  Simplification 
and reliability are paramount; I prefer the use of single point pressure 
reduction over master PRV’s (as do just about all fire departments) but that 
approach is measurably more expensive.

Back story: pressure reducing hose and control valves are listed for 400-500 
PSI, so 350 is just a number that has been carried over from much older 
versions of the standard.  When we tried to completely remove the pressure 
limit from the standard in the early 2000’s, we got hit with amending motions 
on the floor of two code hearings.  The major objection came from the pump 
people because the standard still required a separate pump for each zone at 
that time.  The TC lost the first one so we came up with the express main 
definition and the master PRV prescriptives and got it passed into the 2007 
edition for the first time.   I do not see any reason why there should be a 
pressure limit on any part of a standpipe system.  There is even a 600 PSI FDC 
available from Dixon.

This is absolutely my opinion only.  However, as chair of the TC, I definitely 
have an agenda and this will be tasked in our 2019 Pre-First Draft meeting.

SL


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Daniel Wilder
Sent: Wednesday, August 03, 2016 5:27 AM
To: [email protected]
Subject: RE: HIGH RISE BUILDING

Are we talking Standpipe/Express Mains or the actual sprinkler system itself?

Not sure what edition you are working from but 7.2.1 allows up to 350 PSI for 
any point in the system and over 350 PSI for express mains (7.2.2/7.2.2.1) out 
of NFPA 14 2010 up to the current 2016.

The Sprinkler Age Edition had a lot of good info as well that may be of use for 
your AHJ.

http://reader.mediawiremobile.com/AFSA/issues/105223/viewer?page=17

Dan


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dewayne Martinez
Sent: Tuesday, August 2, 2016 5:44 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: HIGH RISE BUILDING

So when it says "sprinkler pipe maximum working pressure" I can ignore it?  How 
do I get this past the reviewer?

Sent from my iPhone

On Aug 2, 2016, at 7:25 PM, Steve Leyton 
<[email protected]<mailto:[email protected]>> wrote:
Okay, time to go outside the box -schedule 10 and 40 piping isn’t required to 
be listed …   ASTM A53B black steel schedule 40 has is rated for working 
pressures of 430 PSI (4”) and 696 PSI (6”).  And those are with welded joints.  
Vic has what … 700 PSI working pressure for the Style 77 (or something like 
that)?   Far and away the hardest equipment to find is valves that act directly 
on the maximum discharge pressure.

SL

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dewayne Martinez
Sent: Tuesday, August 02, 2016 5:17 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: HIGH RISE BUILDING

Thanks for the information. What did you do for the 300psi limit on pipe?

Sent from my iPhone

On Aug 2, 2016, at 6:36 PM, Steve Leyton 
<[email protected]<mailto:[email protected]>> wrote:
We made 360 total head at churn if I recall correctly.  Everything downstream 
UL (USA) listed for fire – had to hunt down check and butterfly valves from 
Victaulic rated for 365.   Here in CA all high-rises have tanks, so PSH of 
about 7’ + pump rating at max churn.   Big pump yes, but not a monster as it 
was only a 750.  We had three or four stairs in the basement and podium levels, 
so designed to a couple of points on the curve.   We’ve done foam underwing 
systems for Navy and Marine Corp hangars with .17/15,000 flowing concurrently 
at the roof with total demand of 4,500-5,000 GPM.   Now THOSE are big pumps.

SL

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Tom Duross
Sent: Tuesday, August 02, 2016 4:21 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: HIGH RISE BUILDING

Must have been one hell of a pump.


There is no height limit in latest editions of NFPA 14.   Standpipes that 
directly supply hose connections are limited to 350 PSI (stay tuned for 2019 
cycle on that one) but there is no height or pressure limit on express mains 
that serve upper zones.   Our firm designed a 545’ single zone system for a 
tower here in San Diego.


The foregoing is my opinion only and is not intended to represent the NFPA 14 
Technical Committee, nor serve as an interpretation of the standard.

Steve L.
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to