For a standpipe system, show them Table 4.2.1.

SL

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dewayne Martinez
Sent: Tuesday, August 02, 2016 5:44 PM
To: [email protected]
Subject: Re: HIGH RISE BUILDING

So when it says "sprinkler pipe maximum working pressure" I can ignore it?  How 
do I get this past the reviewer?

Sent from my iPhone

On Aug 2, 2016, at 7:25 PM, Steve Leyton 
<[email protected]<mailto:[email protected]>> wrote:
Okay, time to go outside the box -schedule 10 and 40 piping isn’t required to 
be listed …   ASTM A53B black steel schedule 40 has is rated for working 
pressures of 430 PSI (4”) and 696 PSI (6”).  And those are with welded joints.  
Vic has what … 700 PSI working pressure for the Style 77 (or something like 
that)?   Far and away the hardest equipment to find is valves that act directly 
on the maximum discharge pressure.

SL

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dewayne Martinez
Sent: Tuesday, August 02, 2016 5:17 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: HIGH RISE BUILDING

Thanks for the information. What did you do for the 300psi limit on pipe?

Sent from my iPhone

On Aug 2, 2016, at 6:36 PM, Steve Leyton 
<[email protected]<mailto:[email protected]>> wrote:
We made 360 total head at churn if I recall correctly.  Everything downstream 
UL (USA) listed for fire – had to hunt down check and butterfly valves from 
Victaulic rated for 365.   Here in CA all high-rises have tanks, so PSH of 
about 7’ + pump rating at max churn.   Big pump yes, but not a monster as it 
was only a 750.  We had three or four stairs in the basement and podium levels, 
so designed to a couple of points on the curve.   We’ve done foam underwing 
systems for Navy and Marine Corp hangars with .17/15,000 flowing concurrently 
at the roof with total demand of 4,500-5,000 GPM.   Now THOSE are big pumps.

SL

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Tom Duross
Sent: Tuesday, August 02, 2016 4:21 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: HIGH RISE BUILDING

Must have been one hell of a pump.


There is no height limit in latest editions of NFPA 14.   Standpipes that 
directly supply hose connections are limited to 350 PSI (stay tuned for 2019 
cycle on that one) but there is no height or pressure limit on express mains 
that serve upper zones.   Our firm designed a 545’ single zone system for a 
tower here in San Diego.


The foregoing is my opinion only and is not intended to represent the NFPA 14 
Technical Committee, nor serve as an interpretation of the standard.

Steve L.
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to