The standpipe itself.  When you look at a cut sheet for sprinkler pipe it
states that the maximum working pressure is 300psi.  I see Steve’s point
that sprinkler pipe does not have to be listed.  I was just confused by the
mfg’s cut sheet.  Thanks for all the information.



*From:* Sprinklerforum [mailto:
[email protected]] *On Behalf Of *Daniel Wilder
*Sent:* Wednesday, August 03, 2016 7:27 AM
*To:* [email protected]
*Subject:* RE: HIGH RISE BUILDING



Are we talking Standpipe/Express Mains or the actual sprinkler system
itself?



Not sure what edition you are working from but 7.2.1 allows up to 350 PSI
for any point in the system and over 350 PSI for express mains (7.2.2/
7.2.2.1) out of NFPA 14 2010 up to the current 2016.



The Sprinkler Age Edition had a lot of good info as well that may be of use
for your AHJ.



http://reader.mediawiremobile.com/AFSA/issues/105223/viewer?page=17



Dan





*From:* Sprinklerforum [
mailto:[email protected]
<[email protected]>] *On Behalf Of *Dewayne
Martinez
*Sent:* Tuesday, August 2, 2016 5:44 PM
*To:* [email protected]
*Subject:* Re: HIGH RISE BUILDING



So when it says "sprinkler pipe maximum working pressure" I can ignore it?
How do I get this past the reviewer?

Sent from my iPhone


On Aug 2, 2016, at 7:25 PM, Steve Leyton <[email protected]> wrote:

Okay, time to go outside the box -schedule 10 and 40 piping isn’t required
to be listed …   ASTM A53B black steel schedule 40 has is rated for working
pressures of 430 PSI (4”) and 696 PSI (6”).  And those are with welded
joints.  Vic has what … 700 PSI working pressure for the Style 77 (or
something like that)?   Far and away the hardest equipment to find is
valves that act directly on the maximum discharge pressure.



SL



*From:* Sprinklerforum [
mailto:[email protected]
<[email protected]>] *On Behalf Of *Dewayne
Martinez
*Sent:* Tuesday, August 02, 2016 5:17 PM
*To:* [email protected]
*Subject:* Re: HIGH RISE BUILDING



Thanks for the information. What did you do for the 300psi limit on pipe?

Sent from my iPhone


On Aug 2, 2016, at 6:36 PM, Steve Leyton <[email protected]> wrote:

We made 360 total head at churn if I recall correctly.  Everything
downstream UL (USA) listed for fire – had to hunt down check and butterfly
valves from Victaulic rated for 365.   Here in CA all high-rises have
tanks, so PSH of about 7’ + pump rating at max churn.   Big pump yes, but
not a monster as it was only a 750.  We had three or four stairs in the
basement and podium levels, so designed to a couple of points on the
curve.   We’ve done foam underwing systems for Navy and Marine Corp hangars
with .17/15,000 flowing concurrently at the roof with total demand of
4,500-5,000 GPM.   Now THOSE are big pumps.



SL



*From:* Sprinklerforum [
mailto:[email protected]
<[email protected]>] *On Behalf Of *Tom Duross
*Sent:* Tuesday, August 02, 2016 4:21 PM
*To:* [email protected]
*Subject:* RE: HIGH RISE BUILDING



Must have been one hell of a pump.





There is no height limit in latest editions of NFPA 14.   Standpipes that
directly supply hose connections are limited to 350 PSI (stay tuned for
2019 cycle on that one) but there is no height or pressure limit on express
mains that serve upper zones.   Our firm designed a 545’ single zone system
for a tower here in San Diego.



The foregoing is my opinion only and is not intended to represent the NFPA
14 Technical Committee, nor serve as an interpretation of the standard.



Steve L.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to