Hi Don,

Thanks for responding. I checked out the RSV-1 from Tyco and the list price is 
$1,000.00. I about fell out of my chair. It is on the sprinkler riser with a 
branch off to the domestic. When fire sprinklers flow the pressure change 
causes the valve to shut off the domestic. It is non-electric, maybe that is 
why it is so expensive. It has been years but the one I have seen was a simple 
solenoid valve that is attached to the domestic water and simply closes when it 
receives an electric current from the activated flow switch.  HELP anybody!


Owen Evans



-----Original Message-----
From: Don Casey <[email protected]>
To: sprinklerforum <[email protected]>
Sent: Wed, Aug 3, 2016 10:20 am
Subject: RE: Solenoid Valve for domestic side of 13D system riser



Check out Tyco’s RSV-1 valve
 
From: Sprinklerforum [mailto:[email protected]]On 
Behalf Of Owen Evans
Sent: 2016/08/03 1:17 PM
To: [email protected]
Subject: Solenoid Valve for domestic side of 13D system riser
 

Hello Folks,

 

Anybody have a source in southern California where I can get a 1" electric 
solenoid valve to shut off domestic flow (activated by the flow switch)? This 
is so I can eliminate the 5 gpm from the 13D calculations.

 

Thank you,

Owen Evans



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to