Brad

Thank for the rational analysis. How did you arrive how much water the trees 
had on board? They start off quite dry and take up quite a bit of water the 
first day or two.

Experience says that trees throw off embers and are ignited by same, especially 
if being pre-heated. I would be leery of a convection and radiant heat model 
covering this adequately.

Best

Bruce Verhei

> On Sep 6, 2016, at 07:01, Brad Casterline <[email protected]> wrote:
> 
> https://www.dropbox.com/s/jri62zfn4zvulia/Tim%27s%20Trees.pdf?dl=0
>  
> For what it is worth!
>  
> Thanks for the excellent sprinkler challenge Tim!!!
>  
> Brad Casterline, NICET IV
> Fire Protection Division
>  
> FSC, Inc.
> P: 913-722-3473
> [email protected]
> www.fsc-inc.com
>  
> Engineering Solutions for the Built Environment
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org