The blazemaster technical handbook states that cpvc pipe and fittings are
not approved for installation in combustible concealed specs requiring
sprinklers, as referenced in nfpa 13 unless protected by sprinklers
specifically listed for this application. Further on down, the handbook
talks about use of a CC1 and CC2 combustible concealed space sprinkker.

We all know that concealed spaces of combustible construction are required
to be protected by sprinklers unless an exception is met, which there are
plenty.

My question is this:  the use of non combustible insulation shall not
require sprinkler protection per 8.15.1.2.7.  However, if this exception is
used, is the use of cpvc pipe still permitted since we are using an
exception in 13 that omits the use of the special sprinklers called for in
the combustible concealed space section of the technical handbook?

Zach