You stated CPVC is not permitted in concealed combustible spaces
requiring sprinklers. So, by filling with non-combustible insulation,
you now have a concealed space that does not require sprinklers.
Therefore, CVPC would be permitted.
That is at least how I have always found it to be.
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack
On 9/13/2016 2:23 PM, Zachary Siegrist wrote:
The blazemaster technical handbook states that cpvc pipe and fittings
are not approved for installation in combustible concealed specs
requiring sprinklers, as referenced in nfpa 13 unless protected by
sprinklers specifically listed for this application. Further on down,
the handbook talks about use of a CC1 and CC2 combustible concealed
space sprinkker.
We all know that concealed spaces of combustible construction are
required to be protected by sprinklers unless an exception is met,
which there are plenty.
My question is this: the use of non combustible insulation shall not
require sprinkler protection per 8.15.1.2.7. However, if this
exception is used, is the use of cpvc pipe still permitted since we
are using an exception in 13 that omits the use of the special
sprinklers called for in the combustible concealed space section of
the technical handbook?
Zach
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org