Thank you.  I'm seeing it that way as well.

On Tuesday, September 13, 2016, Travis Mack, SET <[email protected]>
wrote:

> You stated CPVC is not permitted in concealed combustible spaces requiring
> sprinklers.  So, by filling with non-combustible insulation, you now have a
> concealed space that does not require sprinklers.  Therefore, CVPC  would
> be permitted.
>
> That is at least how I have always found it to be.
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107email:[email protected] 
> <javascript:_e(%7B%7D,'cvml','email:[email protected]');>
> http://www.mfpdesign.comhttps://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> LinkedIn: https://www.linkedin.com/in/travismack
>
> On 9/13/2016 2:23 PM, Zachary Siegrist wrote:
>
> The blazemaster technical handbook states that cpvc pipe and fittings are
> not approved for installation in combustible concealed specs requiring
> sprinklers, as referenced in nfpa 13 unless protected by sprinklers
> specifically listed for this application. Further on down, the handbook
> talks about use of a CC1 and CC2 combustible concealed space sprinkker.
>
> We all know that concealed spaces of combustible construction are required
> to be protected by sprinklers unless an exception is met, which there are
> plenty.
>
> My question is this:  the use of non combustible insulation shall not
> require sprinkler protection per 8.15.1.2.7.  However, if this exception is
> used, is the use of cpvc pipe still permitted since we are using an
> exception in 13 that omits the use of the special sprinklers called for in
> the combustible concealed space section of the technical handbook?
>
> Zach
>
>
> _______________________________________________
> Sprinklerforum mailing [email protected] 
> <javascript:_e(%7B%7D,'cvml','[email protected]');>http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
_______________________________________________
Sprinklerforum mailing list