I'm thinking the most demanding area would be round (like it was on day one of calcs) with a minimum radius of:
SQRT (1500/PI)=21.85 ft. (if it was LH or OH, >20 ft C.H.) 13 doesn't address curved ceilings, but 72 does, for using heat detectors. Brad On Oct 6, 2016 2:58 PM, "Maurice Marvi" <[email protected]> wrote: > Repairing buried CPVC branch lines sounds like fun. > Not. > > Maurice Marvi > > ------------------------------ > *From*: "Ben Young" <[email protected]> > *Sent*: Thursday, October 06, 2016 3:18 PM > *To*: "[email protected]" <sprinklerforum@lists. > firesprinkler.org> > *Subject*: Monolithic domes > > Does anyone have any information at all about putting sprinklers in a > concrete monolithic dome? > > I was able to find one article about it at the monolithic dome institute's > website here: > http://static.monolithic.com/construction/sprinklers/index.html > > Looks crazy, but also interesting. > > Benjamin Young > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler. > org > >